The way I see it - there is little performance issue of the additional length to get to the right place (code wise) if it is an electrode - it's covered by today's code - if it's not an electrode - it's still covered by today's code.However, if that assumption is a false one, depending on an electrode that isn't one could be an issue, too.
If an inspector can say "Unless you expose 10' of pipe for me to see, we can't assume it's an electrode," so can we.
I believe it's less hazardous to be wrong treating it like it's not an electrode than being wrong treating it as one.
The shortest pathway between the electrical system bonding point and the metallic water system is the best pathway.
So let me get this straight - a 10' + stick of 1/2" copper exiting the building, and going underground complies as the water ground????You can use any water pipe handy that has 10 foot of direct contact with the earth anywhere if you make your connection to said electrode outside. You are not required by the nec to connect within 5 foot of the entrance of the pipe into the building at all, unless you are connecting INSIDE the structure.
Sounded that way????Mark I do not think he is talking about 'any pipe' or a pipe 'exiting' the building.
I believe he is pointing out that you could connect to the water supply line anywhere outside the building that was accessible.
Mark I do not think he is talking about 'any pipe' or a pipe 'exiting' the building.
I believe he is pointing out that you could connect to the water supply line anywhere outside the building that was accessible.
Actually Bob, I am talking about connecting to any 10 ft or longer buried water pipe that is exiting from the ground outside, not just any pipe protruding from the inside to the outside. Its my belief that those water pipes satisfy the rules for grounding electrodes and connecting to them on the outside of the building satisfies 250.52 .
What is common around my area is lots of exterior spigots are run around the outside of the footing in copper lines and a verticle riser comes off the main run to the individual spigots. Those pipes usually are in contact with earth for ten feet or more. Why go to the other side of the structure when some water pipe such as that is available nearby. Something to watch out for is that plastic sleeve the plumbers sometimes put over the water pipes they bury.
So let me get this straight - a 10' + stick of 1/2" copper exiting the building, and going underground complies as the water ground????
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
It was the 93 code when this changed BTW... Just looked it up - the wording of the change 'did not allow metal water piping on the interior of the building to be used as a GEC past 5' from the point of entrance'.... I see your point (making the attachment outside on another UG pipe) - but wonder how many inspectors would see it the same. Some might argue that any modifications down the line to the plumbing would allow an opportunity for that pipe to be disconnected from the rest of the plumbing - where it would be doubtful that the MAIN water would be....
And that is - IF you have a convenient 10'+ water line exiting???
Lets look at it this way... (However it does go against my usual thinking and some of my previous arguments in the cases of CEE's which is different IMO.) If you have >10' entering - it is an electrode, and likewise >10' exiting... So now you have TWO ELECETRODES - the interior plumbing is not allowed to be used as a GEC in that very same code. Would you not have to ground to both???macmikeman, the install you describe would be very uncommon in this area (of course, copper piping is uncommon here now, period) but your post enlightened me in that 250.52(A)(1) simply refers to "a metal underground water pipe" and not necessarily the incoming water supply.
LOOK - DUCKS! SHOOT 'EM!The house was built in early 70's so most likely is copper water pipe coming in.
LOOK - DUCKS! SHOOT 'EM!.
In that case it would be reasonably easy to confirm further. Underground tracer and continuity to exposed known bonded items... Yep - it's a duck... :roll: BLAM!OK, you are adding some equipment near a pool and you have to bond it to the bonding grid, you happen across a solid bare conductor coming up and back down into the dirt near the pool.
It looks like a duck, do you bond the new equipment to it and call it a day?
In that case it would be reasonably easy to confirm further. Underground tracer and continuity to exposed known bonded items... Yep - it's a duck... :roll: BLAM!
In the case at hand - he's more than reasonably sure it is an electrode -
just looking for an excuse