davedottcom
Senior Member
Re: Hot Tub sitting on Pavers!
Rrrrrrrrr, foiled again!

Rrrrrrrrr, foiled again!
Dave,Originally posted by davedottcom:
I'm pretty sure it is much cheaper then buying or making a copper grid.
Does the NEC get any more specific about the gauge or size of the Steele being used? [/QB]
Let's see, if my math is correct, it's actually cheaper to add an inground pool and use it's steel instead of building the copper grid!!!Originally posted by jim sutton:
After some thought, I dont know if this would meet 680.26 (C)(1). This section says "the structural reinforcing steel of a concrete pool".
A hot tub would not be a "concrete pool".
I would look into the product above made by ERICO to be on the safe side.
680.42Originally posted by davedottcom:
Where does the NEC require an E-Grid (as I now call it!) for a Hot Tub?
You're right about that Dave, but where in 680.26(C)does it say you dont need a EBG if you dont have a "paved walking surface"?Jim, I don't think a wooden deck would be considered a "paved walking surface" in 680.26(C).
Neither would crushed stone, or grass, or mulch, or astro-turf! I just think the wooden deck might look the best!