Re: Hot Tub sitting on Pavers!
can you please point to the word portable spa or hot tub
680.26 Bonding.
(A) Performance. The bonding required by this section shall be installed to eliminate voltage gradients in the pool area as prescribed.
FPN: This section does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode.
(B) Bonded Parts. The parts specified in 680.26(B)(1) through (B)(5) shall be bonded together.
(1) Metallic Structural Components. All metallic parts of the pool structure, including the reinforcing metal of the pool shell, coping stones, and deck, shall be bonded. The usual steel tie wires shall be considered suitable for bonding the reinforcing steel together, and welding or special clamping shall not be required. These tie wires shall be made tight. If reinforcing steel is effectively insulated by an encapsulating nonconductive compound at the time of manufacture and installation, it shall not be required to be bonded. Where reinforcing steel is encapsulated with a nonconductive compound, provisions shall be made for an alternate means to eliminate voltage gradients that would otherwise be provided by unencapsulated, bonded reinforcing steel.
(2) Underwater Lighting. All forming shells and mounting brackets of no-niche luminaires (fixtures) shall be bonded unless a listed low-voltage lighting system with nonmetallic forming shells not requiring bonding is used.
(3) Metal Fittings. All metal fittings within or attached to the pool structure shall be bonded. Isolated parts that are not over 100 mm (4 in.) in any dimension and do not penetrate into the pool structure more than 25 mm (1 in.) shall not require bonding.
(4) Electrical Equipment. Metal parts of electrical equipment associated with the pool water circulating system, including pump motors and metal parts of equipment associated with pool covers, including electric motors, shall be bonded. Metal parts of listed equipment incorporating an approved system of double insulation and providing a means for grounding internal nonaccessible, non?current-carrying metal parts shall not be bonded.
Where a double-insulated water-pump motor is installed under the provisions of this rule, a solid 8 AWG copper conductor that is of sufficient length to make a bonding connection to a replacement motor shall be extended from the bonding grid to an accessible point in the motor vicinity. Where there is no connection between the swimming pool bonding grid and the equipment grounding system for the premises, this bonding conductor shall be connected to the equipment grounding conductor of the motor circuit.
(5) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways, metal piping, and all fixed metal parts except those separated from the pool by a permanent barrier shall be bonded that are within the following distances of the pool:
(1) Within 1.5 m (5 ft) horizontally of the inside walls of the pool
(2) Within 3.7 m (12 ft) measured vertically above the maximum water level of the pool, or any observation stands, towers, or platforms, or any diving structures
(C) Common Bonding Grid. The parts specified in 680.26(B) shall be connected to a common bonding grid with a solid copper conductor, insulated, covered, or bare, not smaller than 8 AWG. Connection shall be made by exothermic welding or by pressure connectors or clamps that are labeled as being suitable for the purpose and are of stainless steel, brass, copper, or copper alloy. The common bonding grid shall be permitted to be any of the following:
(1) The structural reinforcing steel of a concrete pool where the reinforcing rods are bonded together by the usual steel tie wires or the equivalent
(2) The wall of a bolted or welded metal pool
(3) A solid copper conductor, insulated, covered, or bare, not smaller than 8 AWG
(4) Rigid metal conduit or intermediate metal conduit of brass or other identified corrosion-resistant metal conduit