chevyx92
Senior Member
- Location
- VA BCH, VA
I agree that it does parallel the neutral, but it's not premises or portable wiring under NEC purview (which stops at the receptacles).
I agree with that.
I agree that it does parallel the neutral, but it's not premises or portable wiring under NEC purview (which stops at the receptacles).
I agree with that.
Not an issue. 300.3(B)(3).Then you've got the circuit-conductors-run-together issue.
...but the premises wiring is not what makes the neutrals wired in parallel. Each neutral is terminated to one receptacle at the load end, so they are not wired in parallel by NEC definition AND scope.The neutrals I was talking about are the premises wiring.
Then you've got the circuit-conductors-run-together issue.
I don't even understand how Larry sees the conductors as not run together.Not an issue. 300.3(B)(3).
Not an issue. 300.3(B)(3).
...but the premises wiring is not what makes the neutrals wired in parallel. Each neutral is terminated to one receptacle at the load end, so they are not wired in parallel by NEC definition AND scope.
Remember, everyone, that's two building receptacles: two hots and two groundeds.Don how do you know the wiring methods between the panel and the buildings receptacle?
And, if only one grounded conductor is used, the other line conductor does not use that circuit's grounded conductor.As soon as you plug the unit in the premises wiring is in parallel and in violation.
I am just assuming that both 30 amp receptacles are in the same pedestal. I don't think any single pedestal is fed with more than one feeder circuit as to do so would violate 225.30.Don how do you know the wiring methods between the panel and the buildings receptacle?
As soon as you plug the unit in the premises wiring is in parallel and in violation.
Note: The YQ100PLUS Adapter
must be plugged into two 50A,
125/250V AC receptacles that are
on the same phase to achieve 100
amp, 125/250 volts power -or- the
“A” leg 50A male into a single 50A,
125/250V AC receptacle to achieve
50 amp, 125/250 volts power.
I disagree. If it is approved by an NRTL it can be used in accordance to the instructions without violation.
Interestingly I do not see any claim that it is listed.
http://www.hubbell-wiring.com/marine/pdf/YQAdapters.pdf
Interestingly I do not see any claim that it is listed.
http://www.hubbell-wiring.com/marine/pdf/YQAdapters.pdf
Can you show me that in the NEC?
Consider this, lets say the two outlets it is plugged into are from seperate transformers, that will result in current flow over the EGCs
I agree it is possible the neutral conductors may conduct in parallel.As soon as you plug the unit in the premises wiring is in parallel and in violation.
I really don't think a company as large as Hubble would produce a none listed product