Inlet on boiler
The last time I checked with Hubbell, their answer was that a three-way switch is not rated to transfer between sources of power. It works fine for transferring loads, but it lacks the internal clearances/insulation required for live source to live source switching.
So I need to turn the breaker off when I change a 3-way for a light?
Could the second path be earth? H/O panel is grounded and so it the transformer on the pole. Not Even 1 little milliamp Bob?
Nope, not one milliamp.
Lets say you have a 9 volt battery as a power source, now you hook up a conductor from one pole of that battery to the neutral in a panel.
Will any current flow in the single conductor?
I would say the majority of 'real' transfer switches do not switch the neutral. In some commercial applications the neutral will be switched for reasons not related to utility personal safety.
Come on, complete your reading :), Well, OK thats where I went.
All devices shall be rated for there service, ETC... , is my continuing thought here.
After drawing it 5 times on paper i got it. i was thinking more of parallel paths to ground
'3-way' is really a 'trade term' for a SPDT.
I don't think a 3 way is a SPDT since it is a single throw (ST) you are only throwing or flipping 1 switch. And as for the pole (s) I'm not sure if you should be able to say SP cause a single pole single throw switch would be an on/off switch, and a DPST would have 4 terminals not 3 like a 3 way has. Maybe a 3 way is technically a APST (alternate pole single throw).
A DPST would only be capable of controlling one power source. A DPDT is like two 3-ways mechanically connected.
I agree.
A DPST (Double Pole, Single Throw) switch has only "ON OFF" positions.
A DPDT (Double Pole, Double Throw) switch has has "ON ON" or "ON OFF ON" positions
A 3-way has one common terminal. That's the Single Pole. It has two traveller terminals. Those are the 2 (Double)Throws. SP+DT = SPDT.
SPDT:
DPST:
DPDT:
A standard three way is in fact a SPST.
The '1 switch' is being thrown between two contacts.
A normal single pole switch is a SPST, one switch being thrown against only one contact.
If you mean 'Throws' = 'Toggle', a 3-way has two : Common to A, Common to B. Two=Double.
it's a single toggle and it can only be changed one time, just like an on/off single pole switch can only go one change or one position change in one motion. Let's say it were a HOA switch, I can see your point there as there is only one toggle switch but you could change the switch to 2 different selections.