No, panel in exact same spot. Also, they are not asking for just GFCI protection on existing outlets, but wanting me to add outlets in kitchen/bath as per 2017 code for kitchens.
p51: There has got to be more to this story. . Is the house all 1950's original? If so that's nuts, every panel change would be a house rewire.
p51 should in no way be liable for unforeseen work the inspector is requiring.
In my state there is a 'grandfather' law that says something to the effect of
wiring installation in existing buildings in the state that complied with the minimum electrical code in effect at the time of installation shall not be considered in violation of the current minimum Electrical Specialty Code standards, unless the use or occupancy of the building is changed
I have done similar panel changes on 1950's homes .
It goes like this I pull the panel cover doing the estimate see only old cloth 2-wire romex (no egc)
and if I get to look around and spot grounded outlets everywhere, and no GFCI's.
I Plug in a plug tester and you guessed it, no ground.
Now in my case since someone in the past replaced a non-grounding outlet with a grounding outlet, that's something that is not grandfathered.
I'll point it out, discuss options with the customer, I tell them
when my inspector sees that he will write up a violation [406.4(D) ] to them, not me.
The inspector is satisfied with stopping at GFCI breakers, despite that to the letter of the code they would not fix it in its entirety as there is 250.114(3) and the whole tamper-proof thing.