Is #6 NM on a 60A breaker code compliance for a Tesla 48A (continuous load) EV charger?

NM cable plants that I know of take raw copper rod and PVC pellets as inputs and only make NM cable.
Even having to do something like print 'THHN' or anything on the cable would involve re-tooling the production line.
Per the UL spec they are allowed lots of flexibility, the only tests it has to pass is the insulation test which it does on the production line.
Here is a video of a NM cable plant
That's fair. I should say that Romex brand NM from Southwire uses THHN/THWN. Other brands may do differently. The Southswire engineer I talked to said, almost exactly, "It's THWN today, but tomorrow it could be something else because the standard is so broad. But at Southwire right now, it's the same stuff you pull in conduit." He made very sure to let me know not to assume it was THHN/THWN, but at the time of our conversation, it was.
 
I should take whomever voted for that amendment on a tour of a SE cable pant, SE cable is made with cross-linked polyethylene (XLPE) insulation type RHW per UL 1581 which has including superior heat and chemical resistance, high insulation resistance, and lower dielectric losses its nothing like the cheap PVC used in NM cable.
SE cable is definitely designed and tested for 75C even when in contact with run in contact with thermal insulation.
Are you referring to USE cable?

SEU and SER use XHHW or THHN/THWN, definetly not RHW.

XHHW was the standard for a long time but in recent years some manufactures have changed to THHN/THWN.
 
Are you referring to USE cable?

SEU and SER use XHHW or THHN/THWN, definetly not RHW.

XHHW was the standard for a long time but in recent years some manufactures have changed to THHN/THWN.
Right my bad , I just took a look at UL 854 section 14.1 it appears to allow SE cable to be a few NEC wire types, THHN / THWN-2 XHHW or RHH/RHW-2 it does not appear to allow the wiggle room that NM cable has, it has to fully comply with UL 44.
 
The conductor insulation on NM cable is the lowest grade PVC that can pass, basically the cheapest plastic blend that can pass UL 719 as electrical insulation. In older NM cable you can sometimes see it marked as type 'TW' . If I recall correctly the PVC blend is only good for 65°C, with short-term exposures to 90°C tested. It does not have any of the additional plasticizers that real THHN / TWHN-2 has to withstand 75°C terminations.
Yet we can start ampacity adjustments with 90C ampacity as long as it is type NM-B which is all that has been made for 35-40 years now so is only a true 60C conductor for older cables when you encounter those.
 
"IF" we allow #6 NM cable to be used in this manner for EVSE, then, would we be able to apply this same kind of thinking for any other continuous loads such as an electric water heater? The resistive elements in a water heater will never draw more than they are actually designed for. This seems to be the apparent logic from DCA.
 
"IF" we allow #6 NM cable to be used in this manner for EVSE, then, would we be able to apply this same kind of thinking for any other continuous loads such as an electric water heater? The resistive elements in a water heater will never draw more than they are actually designed for. This seems to be the apparent logic from DCA.
IMO if they allow it for one thing they basically are saying we no longer have a 60C conductor and therefore should allow it for any other load of similar amp draw. One common place that could get you over the years that many didn't realize is air handlers with heat strips. Most of what were nominally called 10 kW were actually 9.6 kW, and adding a blower motor to the mix usually still left you with MCA below 55 which allowed you to have 6 AWG @ 60C on a 60 amp breaker. Bump the amps up just a little bit by either the blower or the heat strip and it put you over 55 but under 60, still good if using 75C ampacity table but not enough if you had NM cable and had to use 60C ampacity table.
 
NM cable seems to be the wrong tool for the job, its meant to be low cost, every day typical light duty residential installs, nothing wrong with that and I'd imagine changing the PVC formula any higher than 60C (140F) ampacity to be a unnecessary added manufacturing cost that would raise the price of NM across the board.
EV's and other larger continuous residential type loads that need a cable wiring method should look at SE, Tray or MC cable.
I have proposed before that copper 6 SE cable would be best as it would have a 65A rating, good for any 50A continuous load, but some manufacturers don't make it, and the ones that do have small production runs, due to lack of demand.
So if we all go out there and demand it they will start making more of it.
1747072793129.png
 
NM cable seems to be the wrong tool for the job, its meant to be low cost, every day typical light duty residential installs, nothing wrong with that and I'd imagine changing the PVC formula any higher than 60C (140F) ampacity to be a unnecessary added manufacturing cost that would raise the price of NM across the board.
EV's and other larger continuous residential type loads that need a cable wiring method should look at SE, Tray or MC cable.
Eh, the listing standard for NM cable requires an insulation formulation rated for 90C. See this post for an excerpt of UL 719 on NM cable:


The lack of separate listing and labeling of the inner conductors is purely a cost savings measure. The only justification I see for the NEC treating NM cable differently from SER cable would be a claim that its overall durability is lower, and therefore its ampacity should be reduced.

Would be interested to know if the outer jacket of SER cable is thicker/tougher than NM cable. If so, it's a matter of judgement whether that reduced thickness/toughness justifies a reduction in ampacity.

Cheers, Wayne
 
P.S. It is odd that UL 719 4.4.1 prohibits marking the inner conductors if they are made to THHN standards, or made to TW standards using PVC. If a manufacturer wants to mark their NM inners, they must use an insulation that is to TW standards and not PVC. I wonder if anyone does that.