Regarding 690.12 and rapid shutdown on "buildings", does a parking canopy count as a "building"? I don't believe it does, but how would I convince a skeptic that it isn't?
2011 NEC Article 100 said:Building. A structure that stands alone or that is cut off from adjoining structures by fire walls with all openings therein protected by approved fire doors.
That definition seems overly broad, as it make any stand alone structure a building.
Cheers, Wayne
It is intended to be. If you think that is broad, see the definition of structure.Article 100 has a definition:
That definition seems overly broad, as it make any stand alone structure a building.
Cheers, Wayne
Sure, I'm familiar with that. But it seems like the definition of building usually just reduces to that of structure, which isn't so useful.It is intended to be. If you think that is broad, see the definition of structure.
There is the intent of RSS also, it is intended for enclosed buildings, not freestanding frameworks or ground mounted PV arrays.
Understanding Rapid Shutdown
Since the Code language is an installation requirement and not an instruction manual, here I address some of the frequently asked questions regarding rapid shutdown.
Which systems must comply? As stated in the section title, rapid-shutdown requirements apply to PV systems on buildings. If you are installing a roof-mounted PV system subject to NEC 2014, the rapid-shutdown requirements clearly apply to your project. If you are installing a ground-mounted or similar system where none of the PV system components or circuits contacts a building, the rapid-shutdown requirements do not apply.
This does not mean that all ground-mounted PV systems are exempt from rapid-shutdown requirements. Where PV system circuits from a ground-mounted PV system are physically attached to or penetrate a building, you should apply NEC 690.12. However, in this case, the conductors on or entering the building are subject to rapid shutdown, but the conductors off the building are not. Note that underground conductors that travel under buildings are not considered to be “on or in buildings.” Where buried conductors come up into a building, you are allowed to run them a distance of 5 feet from the point of penetration through the floor before installing a disconnecting means.
Sorry, the definition of Building in the NEC is so broad that logically, every structure consists of one or more buildings.The NEC definition is:
Building. A structure that stands alone or that is cut off from adjoining structures by fire walls with all openings therein protected by approved fire doors.
Structure. That which is built or constructed.
Now we get to the logic statement that all buildings are structures but not all structures are buildings.
I am not really interested in people's opinions of intent regardless of who they might be. I am well aware the CMPs actions are public and if I was that curios I would look at them.![]()
Sorry, the definition of Building in the NEC is so broad that logically, every structure consists of one or more buildings.
If that is not the intent, the definition requires updating.
Cheers, Wayne
You code purists probably don't believe in the explanatory notes in the NEC Handbook either. But these provide multiple illustrations of PV array support structures. And the text itself differentiates betweens buildings and structures. So common sense, context, explanatory text, substantiating comments and subject matter expert testimony all point to the fact that structure ≠ building.
Rapid shutdown applies to PV systems on buildings. If it applied to PV systems on structures, it would apply to all PV systems. See the definition of an "array" of Article 690.
If 690.12 applies to all PV systems, why do you think the CMP added the words "on buildings" to the title?
In the event that ambiguous language has been adopted, the intent of the authors is useful in clarifying it, I would say.Right. Because the original intent of the authors is obviously irrelevant to the application of the code in the real world.
What's the justification for having an RSS? I'm pretty certain code does not provide one. Code just requires there to be one under certain conditions. We can debate the conditions but not the justification IMO.Let's back up and ask a substantive question:
Is there an important justification for having rapid shutdown one a parking lot solar canopy structure? Or not?
What's the justification for having an RSS? I'm pretty certain code does not provide one. Code just requires there to be one under certain conditions. We can debate the conditions but not the justification IMO.
That is quite true, and I did not mean to imply otherwise... just meant delving into justification will certainly not resolve whether a parking canopy is a building or not.We are not limited from debating what the code should say.