The haters and doubters will never see the afci as being useful. The fact is they are here and if you hate them then write a proposal to change it but back it up.
:thumbsup:AFCI's would only be $12 if they weren't required.
The haters and doubters will never see the afci as being useful. The fact is they are here and if you hate them then write a proposal to change it but back it up.
The haters and doubters will never see the afci as being useful. The fact is they are here and if you hate them then write a proposal to change it but back it up.
New member here, not from US of A.
You guys who are in the US or other countries dealing with AFCI, have you guys found any real evidence of AFCI have been preventing fire caused by electrical arc (AFCI tripped not because of "noisy" loads or real RFI or ground fault)?
AFAIK, on low voltage 240V or less, loose connections with resistive loads are more likely to produce electrical "spark" than electrical arc (unless there are carbon buildups), do AFCIs also trip when there's electrical "spark"?
Do some AFCIs also "measure" voltage waveform instead of only current waveform to sense electrical arc? I ask this because I've read some AFCI can be tripped from "noisy" loads in different circuit (or line side?).
The haters and doubters will never see the afci as being useful. The fact is they are here and if you hate them then write a proposal to change it but back it up.
The cost of microcontroller, analog components, and circuit board should be no more than US$ 5, the cost of other parts (selenoid, metal connectors and contacs, wires, enclosure/cover) and the assembling cost should be the around the same as GFCI.
I don't think (I could be wrong on this part) the cost for "research and development" for a device "that only measure waveform" is very expensive.
huge profit there.
If AFCIs don't really work like they're supposed to be, what prevent you guys (not just electrical guys, but also customers who paid for "fake safety devices") from filing a class action lawsuit?
Because they aren't useful. I wouldn't put faith into an empty fire extinguisher.
Here is how they are supposed respond to series arcing:
https://www.youtube.com/watch?v=2TWZE1X5fFQ&feature=youtu.be&t=72
Same carbon arc test replicated (this should trip in a less then a second according to IEC 62606):
https://youtu.be/jPlOudTIeGc?t=42
You and Peter have made claims on every afci thread but neither of you, afaik have done anything to try and change things.
But that is kinda like the "Snickers bar" argument: I put a Snickers bar on top of every box on rough in, someone says that is stupid, then I say " well prove to me it's not beneficial."
The haters and doubters will never see the afci as being useful. The fact is they are here and if you hate them then write a proposal to change it but back it up.
Suggestions for solving issues with AFCI installations should be addressed but nothing else.
It's clear you are describing yourself.If the manufacturers have no clarity as to it's function, how do you expect anyone to guide troubleshooting past conjecture?
~RJ~
210.12 probably assumed the all time record rop's ever during the '14 cycle.
These were from none other than Joe Engel (phd EE nema afci-task force chair) and Bob Huddleston (NFPA EE) ,along with multitudes of what you call 'haters'
All were summarily dismissed w/out substainiation , it's like cmp-2 didn't even bother to read them.
Further, CMP-2 has had the same pro-afci seats and/or alternates for over 2 deacdes, manufacture reps, Ul reps, CSPC reps.
As my french friend says it's all 'screwed down'
What needs to be asked , is how many of them own stocks in the market.
~RJ~
X. The UL “Fire Curve”
An examination of Fig. 10 shows that UL labeled the x-axis as “Available short-circuit current (A)”, not load current. The test circuit is shown in Fig. 11; a cord specimen ready for testing is shown in Fig. 12. There was no load connected to the cord (SPT-2). The resistor shown was used to adjust the available short-circuit current from a low of 1A to a high of 100A. The UL engineer acknowledged that he performed parallel arcing tests, not the series arcing tests he was funded to conduct.
So the wire sample is prepared as a parallel, not a series, fault.
The UL engineer acknowledged that he performed parallel arcing tests, not the series arcing tests he was funded to conduct.
I'm not going to choose side here, just wishing no AFCI requirement in my country until at least they're cheap, capable to detect all kind of arc faults, and no false tripping.
Regarding the document by Dr Joe Engel.
Did you spot one small error here?
Quoted from the pdf doc (page 10):
If we see the resistor as a long wire, then yes he was right that it was parallel arc fault.
Now let's try to see the resistor as a reisistive load;
Current flow:
From source > good conductor > load (resistor) > bad conductor > back to source.
We now see it as series arc fault on return path (neutral conductor).
Since it's alternating current, we can also see the current travel backward;
From source > bad conductor > load (resistor) > good conductor > back to source.
The real problem that I saw wasn't the author's small error, but this part:
He was ...
... it's far above my paygrade.
I'm not going to choose side here, just wishing no AFCI requirement in my country until at least they're cheap, capable to detect all kind of arc faults, and no false tripping.
Regarding the document by Dr Joe Engel.
Did you spot one small error here?
Quoted from the pdf doc (page 10):
If we see the resistor as a long wire, then yes he was right that it was parallel arc fault.
Now let's try to see the resistor as a reisistive load;
Current flow:
From source > good conductor > load (resistor) > bad conductor > back to source.
We now see it as series arc fault on return path (neutral conductor).
Since it's alternating current, we can also see the current travel backward;
From source > bad conductor > load (resistor) > good conductor > back to source.
The real problem that I saw wasn't the author's small error, but this part:
He was ...
... it's far above my paygrade.
Your breakers and RCD already detect all arc faults except series arc faults and have been doing so for 60 years. UL went out of their way researching foreign power system, loop impedance and European circuit breakers before they came to the AFCIs recommendation here in North America.
Here is one of their inspirations:
https://paceforensic.com/pdfs/Circuit_Breakers_The_Myth_of_Safety.pdf
http://paceforensic.com/arcing-fault-circuit-interruptor-breakers
http://paceforensic.com/pdfs/newsletter/KeepingPace-15.pdf
http://paceforensic.com/pdfs/newsletter/KeepingPace-37.pdf
http://paceforensic.com/pdfs/newsletter/KeepingPace-7.pdf
In fact the very first AFCIs were intended to be circuit breakers with a 200amp magnetic pickup. However, the debate ensued that certain dwellings will have less than 200amps short circuit current, estimated down to 75amps, and as such electronics took over from there.
My point being that line to neutral and line to ground arc fault protection means nothing when advertised outside North America because the IEC already takes care of that through its existing codes and equipment.
You and Peter have made claims on every afci thread but neither of you, afaik have done anything to try and change things.