I cannot understand why the compulsion of electrical inspectors to have to require even more stupid solutions to easily fixed issues if common sense is applied.

On the other hand, If I was the inspector , I would have made the resident either install a pop up in the counter or else install some cabinets,

I think you contradicted yourself.


Sent from my iPhone using Tapatalk
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
It doesn't matter if it's just a table or a bunch of cabinets. It's a kitchen work surface, a countertop. Countertops require receptacles. Unless the case can be made that it's strictly a dining table. It better be at chair height and surrounded by chairs then.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
In 2017, the title of 210.52(C) was changed to "Countertops and Work Surfaces."

Cheers, Wayne
And it looks like in 2017 they weren't considered to be the same:

" 210.52(C)(2) Island Countertop Spaces. At least one receptacle shall be installed at each island countertop space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. "

Then in 2020, they were considered to be the same:

" (a) At least one receptacle outlet shall be provided for the first 0.84 m2 (9 ft2), or fraction thereof, of the countertop or work surface. A receptacle outlet shall be provided for every additional 1.7 m2 (18 ft2), or fraction thereof, of the countertop or work surface. "
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Those portable work surfaces for kitchens are common for catering events, and commercial kitchens. They get put away after the event, and use extension cords per 590.4(C thru E)

For more permanent ones, our AHJ's recommend a floor receptacle for the cord & plug. Slightly raised or in-use WP floor covers don't collect water
 
Last edited:

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Whats wrong with AHJ's making the determination for temporary, the same way they determine if a wiring method is subject to damage?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I would have tried to get the wire and outlet embedded in the post. You know one day down the road they will want to plug something in regardless of a code issue possibly not requiring one.

I did a job recently that involves recessing receptacles into posts; they were engineered 6x6’s with a hollow core. I fished the cables down the hollow center and cut the outlet box into the 6x6. I discussed with the manufacturer beforehand to make sure this didn’t cause structural issues and was told it wouldn’t be an issue. Finished product looked so much nicer than surface mounted raceway & box.


Sent from my iPhone using Tapatalk
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Lots of opinions here and I appreciate everyone sharing.

I’ll come back and share a pic of the finished product when the “island” is done. Right now just the posts are installed with bracing.


I don’t like the floor box, but it was satisfactory to the inspector and homeowner.


Sent from my iPhone using Tapatalk
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
I think the inspector missed 210.52(C)(5) exception that the receptacle placement if cannot be within the 20 in above countertop or work surface that it can be below but must be within 12 inches. That would make for an awfully low island if receptacle is in floor. Practical solution would be similar to one that @brantmacga had said in post #33.
Code also makes no reference to a "cabinet" but uses term "support base", that can be simply pillars.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I think the inspector missed 210.52(C)(5) exception that the receptacle placement if cannot be within the 20 in above countertop or work surface that it can be below but must be within 12 inches.

Inspector didn’t miss it, just compromised with homeowner who was adamant he would not have an island recep.


Sent from my iPhone using Tapatalk
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Inspector didn’t miss it, just compromised with homeowner who was adamant he would not have an island recep.
That would be nice to be able to do. "You two let me know when you come up with a solution acceptable to both of you."
 

kwired

Electron manager
Location
NE Nebraska
I cannot understand why the compulsion of electrical inspectors to have to require even more stupid solutions to easily fixed issues if common sense is applied. On the other hand, If I was the inspector , I would have made the resident either install a pop up in the counter or else install some cabinets, simply because the concept of the 4 posts and a countertop is so outlandishly stupid and ugly in the first place. Not because of any internal obligation to enforce a silly ass code some how or another. By the way, last time I checked, 4 legs and a top is called a table not an island. Talk the owner into not attaching it at the leg bottoms and you don't have an Island countertop.
We have a winner, it is now a table. If they really want to attach them after passing inspection they can then do so.
 