A microwave that is not also a range hood and is located "In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit" and is cord an plug connected will be connected to a SABC, even if a dedicated circuit, code defines this as a SABC.
210.52 is titled Dwelling Unit Receptacle Outlets.
210.52(B)(1) is about "receptacle" outlets. Anything not supplied through a receptacle outlet is not included in 210.52(B)(1).
We also have Infinity's mention of 422.16(B)(4) and the requirement if the hood is cord and plug supplied that it must be on an individual branch circuit. This individual circuit is still a SABC. You could have this and one more SABC and meet your minimum of two required SABC's. That second circuit could also supply all the receptacles in the dining room, pantry, or other similar areas and still be code compliant.
210.52 is titled Dwelling Unit Receptacle Outlets.
210.52(B)(1) is about "receptacle" outlets. Anything not supplied through a receptacle outlet is not included in 210.52(B)(1).
We also have Infinity's mention of 422.16(B)(4) and the requirement if the hood is cord and plug supplied that it must be on an individual branch circuit. This individual circuit is still a SABC. You could have this and one more SABC and meet your minimum of two required SABC's. That second circuit could also supply all the receptacles in the dining room, pantry, or other similar areas and still be code compliant.