Nobody has said that the manufacturer rates the fixtures this way (not yet, anyway). So let's not presume what is not yet known.
Not a presumption. OP indicated this in post 38, otherwise I wouldn’t have mentioned it.
Nobody has said that the manufacturer rates the fixtures this way (not yet, anyway). So let's not presume what is not yet known.
Not a presumption. OP indicated this in post 38, otherwise I wouldn’t have mentioned it.
Not a presumption. OP indicated this in post 38, otherwise I wouldn’t have mentioned it.
210.23(B) was originally intended for HID lighting, not LED's which by default fall into "utilization equipment in any occupancy..." I.e.they're not lamp.
I've installed 30A branch circuits in lighting panels throughout heavy industry and never had a problem selling it to inspectors. 210.23(B) was originally intended for HID lighting, not LED's which by default fall into "utilization equipment in any occupancy..." I.e.they're not lamp. NEC 210.20(B) is the real key to protecting lighting circuits. Article 404 needs to be reviewed for switching devices. All need to be rated 30A including the fixture.
I don't believe he was saying that the manufacturer states that the fixture can be supplied by a 30A fixture in post 38.
How is it not a fixed lighting unit?
NEC is a guideline for electrical safety. OP has the branch adequately protected with correctly sized wire (provided no 'derates' apply) and everything is rated for 30A. Arguing over a definition that is vague at best seems absurd, but that's just me.
How do you know the fixture is rated for 30A?
The Code is clear what type of fixed lighting unit can be supplied by a 30A circuit. Arguing that you can ignore that Code section seems absurd to me.
How do you know the fixture is rated for 30A?
The Code is clear what type of fixed lighting unit can be supplied by a 30A circuit. Arguing that you can ignore that Code section seems absurd to me.
The code is clearly not clear about LED's. If it were, this string would have ended many posts ago. Making a case over the definition of heavy-duty lamp-holders is incredibly weak. The intent of the Code has been met provided the OP resurfaces with proof of a 30A rated LED.
Do LED luminaires even have a lampholder?
The code is clearly not clear about LED's. If it were, this string would have ended many posts ago. Making a case over the definition of heavy-duty lamp-holders is incredibly weak. The intent of the Code has been met provided the OP resurfaces with proof of a 30A rated LED.
The Code is completely clear. This string would have ended many posts ago if people weren't trying to find excuses for ignoring what the Code say. (And the only person making an argument over the definition of heavy-duty lampholder is the OP.)
The intent of the Code will not be met if the OP resurfaces with proof of a 30A rated LED. The intent of the Code would only be met if the OP resurfaces with proof of an LED fixture with heavy-duty lampholders...which of course, he won't, because LED lighting units don't have heavy-duty lamp holders.
The LED can't have a heavy-duty lampholder because its not a lamp. If OP comes back with a vendor document that shows a 30A rated LED the intent of the Code will have been met.
And if it can't have a heavy-duty lampholder, it can't be supplied by a 30A circuit by Code. It's not really complicated.
unless of course its utilization equipment - see definition, Art 100; not complicated at all.
So you just want to ignore the first part of 230.23(B)? Ignoring Code sections is generally not a good idea.
For a fixed lighting unit to be supplied by a 30A circuit, it must have heavy duty lampholders and it must not be in a dwelling unit.