they do not agree with you
they require gfci in many locations
homes first, then expanded to other occupancies
you miss the point
when wet you may bypass the egc, become the gf path
and even with an egc it may limit i < the threadhold, where as without it you may die
it is good you accept facts
not in all, or even most scenarios where the person is/initiates the fault
Yup- which can be used to calculate body current for a given voltage. That given voltage comes from knowing your fault circuit Z.
not saying it is required
but big benefit for low cost although risk is only low/moderate, not high
Historically GFCI has mostly only been required for receptacle outlets. I believe the reason is higher risk of a compromised EGC.
Even now with commercial kitchens, it is still only for receptacles as the general rule. If you have a choice of "hardwiring" vs "cord and Plug" on a particular appliance -the hardwired installation won't require GFCI. Now in 2017 NEC they added more receptacles as well. I don't necessarily agree that they needed to add all of them but still is only for receptacle outlets.
And IMO the 5-15 and 5-20 cord caps are the worst for losing the EGC pin. Sure there is intentional removal of them on occasion, but they do end up breaking off easier from mishandling then the EGC of almost any other plug type, and I believe this is part of why GFCI protection expanded to most of the locations it did, along with many of those locations having higher possibility of contact with a grounded surface.True- commercial kitchens often end up with missing ground pins. One of the most eye opening threads:
http://forums.mikeholt.com/showthread.php?t=172466&p=1682020#post1682020
Note that 590.6(B) does not apply to 125 volt, 15, 20 or 30 amp receptacle outlets. You are not permitted to use the assured equipment grounding program in lieu of GFCI protection for 125 volt, 15, 20 or 30 amp receptacle outlets.
And IMO the 5-15 and 5-20 cord caps are the worst for losing the EGC pin. Sure there is intentional removal of them on occasion, but they do end up breaking off easier from mishandling then the EGC of almost any other plug type, and I believe this is part of why GFCI protection expanded to most of the locations it did, along with many of those locations having higher possibility of contact with a grounded surface.
Used to be exceptions to some GFCI's if you could prove you had an assured EGC program, which also indicates that a compromised EGC was recognized as a problem here. Was still probably easier to use GFCI's then to implement a program to assure all the EGC's are intact. OSHA probably still wants to see EGC's intact though.
590.6(B)(2) only applies to certain circuits. Not that I have ever seen implemented on the job site anyways. Way too much trouble IMO.
And if were to implemented, it does not apply to GP circuits on a construction site.
From don g in a another thread on this topic:
GFCIs have less to do with water and more to do with EGCs in terms of what got them into the code and helped them spread.
Instead of posting all that extraneous stuff, you could have simply stated that idea and we discuss it.
Simpler to just say it -than post links, graphs, and what not that is distracting.
I did on my first post in this thread, here:
http://forums.mikeholt.com/showthread.php?t=192766&page=2&p=1932123#post1932123
What came after was the assertion that an EGC is not sufficient protection among others.
Nope.
No such assertions were made.
All said GFCI not required. A few said it was not a bad idea though.
The whole idea of one over the other was your idea, you wanted that spin.
And make no doubt, I am well versed in the history of GFCIs and EGCs, and their NEC development and how they may or may not be intertwined fulfilling their functions.
This argument had nothing to do with any previous assertion in this thread.
wrong
an egc does not prevent shock with a hi z fault
In any case we can agree to disagree if an EGC alone is sufficient protection. Nothing hurts having a GFCI at the lobster tank, but IMO as long as the equipment has an EGC I am not worried about safety to personnel.
Who the heck is disagreeing that an EGC alone is not sufficient protection per NEC?
Not me, Iggy, or anyone else.
Now are there various scenarios in which standard rules apply, or extra protection is needed, or times which one form of protection would be more beneficial? Yes.
Those we can discuss, no problem, but the high z fault mentioned was a conditional excercise.
Not a direct answer to OP.
Now if the OP was to add a GFCI, I'd have no issue. There is nothing wrong with extra protection.
Assertion can be found here:
http://forums.mikeholt.com/showthread.php?t=192766&page=2&p=1932162#post1932162
To which a debate about that started from there.
In any case we can agree to disagree if an EGC alone is sufficient protection. Nothing hurts having a GFCI at the lobster tank, but IMO as long as the equipment has an EGC I am not worried about safety to personnel.
See, we is all in harmony. Good.:thumbsup:
The argument you really wish to discuss has more to do with the 1996 change to 250.140 for ranges and dryers, and/or the history and debate around 250.130 and replacement receptacles in regards to providing an EGC or GFCI protect old 2 wire supplied receptacles.
Well.....I ain’t going there in this thread.