mbrooke
Batteries Included
- United States
- Technician
if what you are saying under a bolted fault 1/2 of the v appears across each conductor (if equal z), so???
The person is exposed to half this V for a few cycles- until the breaker opens.
under hi z, low leakage, the person is in the path, parallel
assume 120/0.05 = 2400 a fault
Add an EGC to the mix and watch how the current from frame to earth plummets.
High Z about a few volts tops until the fault continues.
Low Z about 60 volts max for a few cycles.
Under both conditions the person is not harmed, hence why an EGC alone is permitted in so many code scenarios. High or low Z fault EGC protects.
person sees 0.1/1000 x 2400 = 240 ma
kills in 0.16 sec for a 100 lb person
the gfci would trip much faster and limit it to x ma range
Yup- and IEC 479-1 is a good reference. (sorry for the junky picture, there are better ones out there but not finding them)
https://www.google.com/search?q=fig...UICygC&biw=1440&bih=725#imgrc=vbJ79wccZPekrM: