al hildenbrand
- Minnesota
- Electrical Contractor, Electrical Consultant, Electrical Engineer
:?The code was not created to deal with a brand device.
Armored Grounding Wire, KDER, is NOT a "brand device".
Al,
Do you have a datasheet showing the Armored Grounding Wire already have each end of the armor bonded to the inside copper conductor, or the armor is not ferrous metal? If not then it's just a GEC inside a ferrous enclosure.
Al,
Brian, can you not accept the fact that, under the UL product description the KDER is armored wire, not cable with armor? It is a different category and may therefore be treated differently. Now if the wire inside the armor were insulated (i.e. if the product were in fact cable) then I might reach a different conclusion.
If not, what exactly is the "cable armor" the code talking about?
"Armored Cable," type AC, has been in the NEC since the 1913 edition.
"Armored cable" is not what 250.64 referring to. The code talks about the spiral wound steel sleeve part alone as a flexible steel conduit, not a whole armor cable in AC class.
From Post # 47
Over the decades since 1913, the NEC has a long history of using the two-word term, Cable Armor, in rules about how to treat the spiral wound metal outer covering of the two, or more, insulated conductors within the manufactured cable known an Armored Cable.
cable armor A metallic element or envelope inserted in or around a cable sheath to provide mechanical protection against rodents, severe installation conditions, etc.
Charlie's Rule of Technical Reading
It doesn't say what you think it says, nor what you remember it to have said, nor what you were told that it says, and certainly not what you want it to say, and if by chance you are its author, it doesn't say what you intended it to say. Then what does it say? It says what it says. So if you want to know what it says, stop trying to remember what it says, and don't ask anyone else. Go back and read it, and pay attention as though you were reading it for the first time.
Copyright 2005, Charles E. Beck, P.E., Seattle, WA
Why do you think 250.64 talks about AC class armored cable in the GEC context?
I also think the OP was using an armored grounding wire but failed to bond the steel armor sleeve properly per AHJ. Am I wrong?
I always used MC connectors to connect my armored ground. I used the snap in MC connector. AHJ said it was not properly bonded with that connector, this job was a service change for a solar array, Solar Company drove a ground rod by there disconnect on the other side of house and used a Romex connector with a ground bushing to bond there armored ground and that was properly bonding the MC according to the inspector, I have used Romex connectors on MC but never if the inspector can see it and only has a last resort, My GEC is water then to ground rod #4 it's about a 50 foot run. Does anybody know of a way I can bond the mc
I don't have NEC book.
How would you install it for earth grounding a Service Panel, if you don’t mind to share?
my area also has next to no armored grounding wire in use.
Because of the lack of common usage I would err on entering an enclosure through a listed connector where exposed outside of a structure, but on the interior and a Service Disconnecting Means, where no physical protection is a Code rule, I'd run it as a bare conductor.
Al,
All of the works I had done I should be able to back them up with calculations, product datasheets, industry publications or physics laws if anyone, AHJ included, ever question about their safety, performance, and function. I had asked numerous times for any datasheet, Application Note, or any document that to show the said armored ground wire is approved to be used for GEC without the needs to bond its steel armor ends to the enclosed conductor, or how to install it correctly. Listed under Grounding and Bonding Equipment, KDER, doesn’t mean the product when installed incorrectly and still can be code compliant. How would you install it for earth grounding a Service Panel, if you don’t mind to share?
What you did might be OK with your local regulation, but it might not meet the National Electrical Code at other locals.
Sorry bout the confusion it is metallic cable with with 1 # 6 solid copper wire, I talked to Arlington, they said not only is there MC box connectors, But any manufacturers MC connectors have to be UL listed for 514.B tested for bonding and grounding thanks for the input
The takeaway: Theory only gives you less than passing marks.