That's an interpretation. Read the following portion...
Subpart I?Electrical Systems
? 3280.801 Scope.
(a) Subpart I of this part and Part II of Article 550 of the National Electrical Code (NFPA No. 70?2005) cover the electrical conductors and equipment installed within or on manufactured homes and the conductors that connect manufactured homes to a supply of electricity.
(b) In addition to the requirements of this part and Part II of Article 550 of the National Electrical Code (NFPA No. 70?2005), the applicable portions of other Articles of the National Electrical Code must be followed for electrical installations in manufactured homes. The use of arc-fault breakers under Articles 210.12(A) and (B), 440.65, and 550.25(A) and (B) of the National Electrical Code, NFPA No. 70?2005 is not required. However, if arc-fault breakers are provided, such use must be in accordance with the National Electrical Code, NFPA No. 70?2005. Wherever the requirements of this standard differ from the National Electrical Code, these standards apply.
An interpitation of the above in red, seems pretty clear:happyyes: