I have to disagree, with equal loading on both sides of the neutral it does in fact 'bypass' the neutral. The neutral could be removed with no change at all in the circuit operation.
I tend to agree with Dennis. If the neutral is removed, the circuit will work, but any fluctuations on one of the loads will affect the voltage on the other load where if the neutral is connected, the loads will maintain the voltage independent (except for voltage drop) of the conditions of the other load.
With a neutral you have 2 independent loads, without the neutral have a series circuit.
Nothing ever remains equal. Technically you are correct, but practically, it is a problem.