Ghostbuster, you mentioned that the flux densities around the houses were between 100 to 200 milligauss.
I found some formulas for calculating the magnetic fields around 60 Hz power lines. There is a formula for balanced 3-phase situations, and unbalanced situations. These were found at
http://www.euro-emc.co.uk/datasheets/Magnetic/EMF%20Fundamentals.pdf.
Balanced Phase Equation: B = (3.46 x I x d) / r^2
where
B = flux density in milligauss
I = Amps in each phase
d = distance between phase conductors on towers in meters
r = distance from nearest phase conductor in meters
Unbalanced Current Equation: B = (2 x I) / r
where
B = flux density in milligauss
I = unbalanced amps
r = distance from nearest phase conductor in meters
We know that the transmission line in question had to either be balanced or unbalanced, so let's do some calculations assuming balanced, then unbalanced. Assume RMS values.
If we had balanced phases: We can calculate the current in each phase of the transmission line.
B = (3.46 x I x d) / r^2
Given:
B = 150 = flux density in milligauss (splitting the difference of 100-200)
I = Amps in each phase = unknown, we will solve for this
d = 20 feet = 6 meters = distance between phase conductors on towers in meters (The 6m is an assumption based on visual inspection of typical high tension lines. If you have better data, let me know. How far apart where the phases?)
r = 70 feet = 21.2 meters = distance from nearest phase conductor in meters (again, this is an asumption, assuming the nearest conductor was 60 feet in the air vertically and 40 feet horizontally from the backyard. If you have better data, let me know. I would think the distance was actually further than this.)
150 = (3.46 x I x 6) / 449.4
use basic algebra
I = 3247 amps in each phase at 230 kV 60hz required to produce 150 milligauss at 70 feet
This seems like an awful lot of current on the transmission line. Of course, this is based on my ignorance - I just wouldn't expect it to be that high. So, I researched on the net, and typical current values of 230 kV lines were 200 to 900 amps. I did find one that had an emergency rating of 1600 amps. Do you have data on how much current the 230 kV lines were actually carrying?
Now let's assume there was a current inbalance that was the major contributing factor:
B = (2 x I) / r
Given:
B = 150 = flux density in milligauss (splitting the difference of 100-200)
I = Amps in each phase = unknown, we will solve for this
r = 70 feet = 21.2 meters (same as in previous formula)
150 = (2 x I) / 21.2
basic algebra
I = 1590 amps unbalanced current at 230 kV 60 hz required to produce 150 milligauss at 70 feet.
Again, this seems like an extremely large imbalance to have between phases. I would think the POCO would have noticed this and would have corrected it long ago.
Anyone see any issues above? Ghostbuster? Yes, some of the data is estimated, but surely it is in the ballpark. Of course I have follow-up coming, but I'll wait to see if anyone is still interested in this. The question at the moment is "Could the transmission line currents be THAT high?"