NEC 2014

Merry Christmas
Status
Not open for further replies.

Esthy

Senior Member
Laundry rooms must have GFICs, but if laundry rooms contain only washer, dryer and refrigerator, not laundry sink - this is the commercial facilities where I work and have 15 utilities room - will I need to replace the existing for the GFICs? What about the arc faults?
 
My apologies, I didn't explain better. In only one outlet receptacle: 2 washing machines, 1 refrigerator, 2 detergent/bleach dispensers and sometimes a fan or dehumidifier are crammed with adapters, so I would like to add another circuit and I thought that because of this "upgrade and been in 2014 code" I needed to GFIC them, but reading iwire (good mentor here) comments about 210.8 (B) I see it is not necessary ... correct?
 
If you adding a new circuit , I would think it should be brought up to code.
And if it is non dwelling application - neither GFCI or AFCI is required for the area described. Not too much there that likely needs brought up to code unless it is older then dirt.
 
Gosh I love this forum! Free schooling! Thanks!

Welcome to the forums.

A word of advice - title your threads with a logical, relavent title.
Something along the lines of "GFCI & AFCI requirements in commercial laundry" may get you better results.
 