125% over instantaneous- peak arc impedance limits current to 80% of the available bolted fault current.
Once this met, series arcing is detected and mitigated.
You’re still wrong about what it says. And instantaneous will definitely not detect “series” arcing.
Post #42- statistical analysis shows fault current 125% of the magnetic pickup clears parellel arcing over 99% of the time.
Arcing may be chaotic, but its strike angle and conductance in the sine wave is prolonged enough and of low enough impedance to present significant current magnitudes such that available short circuit current is the predominate predictor of arcing current.