peter d
Senior Member
- Location
- New England
More gibberish nonsense.
install a new Leviton 223-W, or if on old brown paneling, the 223 item.
Either of those receptacles would cause an NEC violation.
Do you have a solution that would actually pass inspection?
your 1-R is busted
210-7(d)(3)
oh, i see, "new" got you hung up. i mean "new" as in buy a new one, replace the old.
did i miss your Q ?
maybe i just missed what your Q wasCan you try posting in complete thoughts?
210-7(d)(3)? What year is this?
The replacement receptacles you suggested would create an NEC violation.
let Mr MH tell you if you are unsure. pay close attention at 32-38 seconds, replay if you need to.
here, let Mr MH tell you if you are unsure. pay close attention at 32-38 seconds, replay if you need to.
What year is this?
my AHJ uses NEC 2011 w/ AHJ amendments. your point is what exactly ??The 2011 NEC? Really?
Most of the country is under the 2014 NEC making that basic concept, of a one-for-one replacement, non-compliant for lack of AFCI in most residential settings where one will still find two wire nongrounding type receptacles still in service.
my AHJ uses NEC 2011 w/ AHJ amendments. your point is what exactly ??
my AHJ uses NEC 2011 w/ AHJ amendments. your point is what exactly ??
That your solution is against the rules under the 2014 b/c of 406.4(D)(4).
ok, nobody asked for specific NEC versions, all that was blanket said was, "its NEC violation", and the answer to that is "no its not".
install a new Leviton 223-W, or if on old brown paneling, the 223 item.
Either of those receptacles would cause an NEC violation.
Do you have a solution that would actually pass inspection?
Slow down and read it again if you don't understand.my AHJ uses NEC 2011 w/ AHJ amendments. your point is what exactly ??The 2011 NEC? Really?
Most of the country is under the 2014 NEC making that basic concept, of a one-for-one replacement, non-compliant for lack of AFCI in most residential settings where one will still find two wire nongrounding type receptacles still in service.
(2011 and later gave an exception for the tamper proof requirement when replacing 2w receptacles)
I am not seeing an exception to 406.4(D)(5).
Where should I be looking? :huh:
I am not seeing an exception to 406.4(D)(5).
Where should I be looking? :huh:
what do you mean re-read it? non-compliant for lack of afci? what? doesnt code say you need to have afci/gfci/tamper proof only if the location of the replacement requires such?[B said:al hildenbrand[/B]] The 2011 NEC? Really?
Most of the country is under the 2014 NEC making that basic concept, of a one-for-one replacement, non-compliant for lack of AFCI in most residential settings where one will still find two wire nongrounding type receptacles still in service.
This quote of 406.4(D)(2)(a) does not exempt one from 406.12.2014 NEC
406.4
(2)Non–Grounding-Type Receptacles.
Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(2)(a), (D)(2)(b), or (D)(2)(c).
A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).