This quote of 406.4(D)(2)(a) does not exempt one from 406.12.
406.4 says a replacement needs to meet 406.12 ?
This quote of 406.4(D)(2)(a) does not exempt one from 406.12.
what do you mean re-read it? non-compliant for lack of afci? what?
The un-amended 2014 NEC requires AFCI protection for the replacement receptacle, in most areas of a dwelling where one commonly finds two wire nongrounding type receptacles still in service.what do you mean re-read it? non-compliant for lack of afci? what? doesnt code say you need to have afci/gfci/tamper proof only if the location of the replacement requires such?
afci is not a requirement, its the exception that must be met.
Yes. 2014 NEC 406.4(D)(5)406.4 says a replacement needs to meet 406.12 ?
406.4 says a replacement needs to meet 406.12 ?
It is fine if he keeps using that stuff...just means I don't pay any attention to what he writesCan't you just say "ungrounded" instead of this 1-R, 5-P stuff? :roll::roll:
Yes. 406.4(D)(5)
What is a "NEC member"? The NEC is just a document....
side Q - does anyone here, perhaps even the NEC members, know how to do Root Cause Analysis backwards, kinda like doing differential equations ?
ok, if they dont make 1-R tamper proof then NEC cannot stop you from doing a 1R for 1R replacement even if the location calls for tamper proof. same concept as NEC saying you can just do 1R to 1R if the location requires GFCI but you cannot fit a GFCI into the mounting box, although not sure if NEC forces GFCI breaker at that point. in the end, AHJ has final say if you permit a replacement 1R :thumbsup:
There is no relief in the 2014 NEC for 406.4(D)(4) AFCI protecting a replacement. You may have some "deal" worked out with your AHJ, but that is not "the un-amended NEC."
..... that requires arc-fault circuit-interrupter protection as specified elsewhere in this Code .....
if the location does not require it, then its not required.
what am i missing?
hmmm, no EGC causes fires. interesting. so having a non-EGC'd GFCI is a fire hazard for 5-p cap corded appliances ?? is NEC missing something ??
https://www.firerecruit.com/articles/1206100-5-common-causes-of-electrical-fires
I regret to say, but FFs are not the best fire forensics experts. As someone with many years in the fire service once told me "Most garden variety FFs can not tell an outlet from their omelet ~CS~"
well, call/name/blame it what/how you want, the NEC is written under NFPA 70, right? but i guess FFs dont know much? which i respectfully disagree.
the article was referencing publication by FEMA's US Fire Administration.
???
if the location does not require it, then its not required.
what am i missing?
well, call/name/blame it what/how you want, the NEC is written under NFPA 70, right? but i guess FFs dont know much? which i respectfully disagree.
the article was referencing publication by FEMA's US Fire Administration.
1) "virtually" means what exactly#1- The fact that virtually the entire dwelling is required to be afci protected,
And by your inference, I guess that the members here who have given you code references, and hashed these threads out w/you must not know much either.
That article you in posted in your op contains blatantly false information about the function of an egc. An egc is not there to "handle the extra amount of electricity appliances draw." And it does not make any difference what organization was purportedly behind that statement- it is, on its face, completely wrong.
1) "virtually" means what exactly-
2) no, others know a lot, i havent said not knowledgeable
3) ok, exactly why i asked the Q in post #1, but the hazard around missing EGC is not "completely wrong"
what else?
the article reference, along with OSHA, doesnt mention "GFCI" in their explanation of the hazard of a 5-P being connected to a 5-R that has missing EGC. and i dont believe i mentioned "GFCI" either.You already know that lack of an egc w/out gfci is a risk for electrocution when 3 prong appliances are used- now how does the lack of an egc contribute to a fire hazard?
the article reference, along with OSHA, doesnt mention "GFCI" in their explanation of the hazard of a 5-P being connected to a 5-R that has missing EGC. and i dont believe i mentioned "GFCI" either.
hmmm, no EGC causes fires. interesting. so having a non-EGC'd GFCI is a fire hazard for 5-p cap corded appliances ?? is NEC missing something ??