Why is TT common in Europe? Are they saving on transformer grounding conductor?
Good question. Honestly, I do not know for sure. However, I do know TT supplies are recommended where the neutral conductor is likely to be disconnected. In trailer parks for example, only TN-S and TT is permitted because a broken PEN or CNE can be very dangerous. In dairy farms and chicken coops TT is good because any voltage drop along the neutral does not place itself on the grounding system. Cows are very sensitive to stray voltage. In France TT is used universally.
Or why didn't they ground one leg (of the two hots) to become the neutral?
One leg grounded. Often its 230/400Y, with homes receiving a neutral and hot, businesses 3 hots and a neutral.
Norway is IT, but thats another story.
In my country. Since 99.99% of homes don't have local grounding electrode and no ground wire direct to transformer, then it's like we are also TT. Or what do you refer to those without even local grounding electrode (are these installed in all homes in Europe with TT transmission system?).
At best it sounds like a system without any grounding. At worst a TT that has not properly been implemented.
TT systems in Europe have a grounding electrode system at the building. The wire from the earth driven rods or plates goes to the ground bar in the panel. All the circuits are RCD protected in some way as that is what will remove a fault. Ground rods vary in resistance, and 2 out of 3 times do not pass enough current to trip a regular breaker or fuse.
I do not know what part of the Philippines you are from, but the Philippine electrical code requires that each structure have a service neutral, one or more ground rods, and a grounding system within the building. Its based on the American NEC, often word for word. Technically everything that you describe is a dozen of more code violations.