I am again repeating myself.
You don't select trip level based on frequency of tripping. You select trip level based on protecting what you want to protect.
If you wish to use residual current detection as the prime protection from electric shock, then you must use a class A GFCI, at 5-6mA. 5-6mA is generally considered the level of no harm from shock.
See https://www.wikilectures.eu/w/Physiological_effect_of_electric_current to understand what happens when current levels go up.
30mA protection is suitable for equipment protection. Also it _may_ reduce shock hazard in the context of proper bonding of metallic equipment. If you have a properly grounded metallic frame appliance, and have a short in the appliance, then the frame gets energized until the OCPD opens. If you have a 30mA RCD, then the frame is only very slightly energized before the RCD opens.
But now imagine you have an _ungrounded_ appliance. Some sort of fault energizes the chassis, but since there is no grounding there is no significant fault current flow, and the RCD has nothing to detect. Now someone touches the frame and ground, the current flows through them. If the current through the person is sufficient, then the RCD opens. However the RCD will not open until the shock is rather severe.
So if you want to protect _people_ in the context of circuits without grounding, then use a class A GFCI, and if you get tripping during normal operation then you should consider the device unsafe. It may not be 'broken', but the device is not safe to be used without proper grounding.
If you want to enhance the protection of your _circuits_ and _appliances_, then go ahead and use 30mA RCD breaker. But this will not provide protection for _people_ from dangerous levels of electric shock. It will reduce the maximum severity of a shock, but would permit a painful shock that is severe enough that a person might not be able to 'let go'.
-Jon
You don't select trip level based on frequency of tripping. You select trip level based on protecting what you want to protect.
If you wish to use residual current detection as the prime protection from electric shock, then you must use a class A GFCI, at 5-6mA. 5-6mA is generally considered the level of no harm from shock.
See https://www.wikilectures.eu/w/Physiological_effect_of_electric_current to understand what happens when current levels go up.
30mA protection is suitable for equipment protection. Also it _may_ reduce shock hazard in the context of proper bonding of metallic equipment. If you have a properly grounded metallic frame appliance, and have a short in the appliance, then the frame gets energized until the OCPD opens. If you have a 30mA RCD, then the frame is only very slightly energized before the RCD opens.
But now imagine you have an _ungrounded_ appliance. Some sort of fault energizes the chassis, but since there is no grounding there is no significant fault current flow, and the RCD has nothing to detect. Now someone touches the frame and ground, the current flows through them. If the current through the person is sufficient, then the RCD opens. However the RCD will not open until the shock is rather severe.
So if you want to protect _people_ in the context of circuits without grounding, then use a class A GFCI, and if you get tripping during normal operation then you should consider the device unsafe. It may not be 'broken', but the device is not safe to be used without proper grounding.
If you want to enhance the protection of your _circuits_ and _appliances_, then go ahead and use 30mA RCD breaker. But this will not provide protection for _people_ from dangerous levels of electric shock. It will reduce the maximum severity of a shock, but would permit a painful shock that is severe enough that a person might not be able to 'let go'.
-Jon