As Adamjama says, a clamp meter uses the basic mechanism of detecting the magnetic flux around a wire to measure current.
I would not trust a random clamp meter for general AC use designed to detect single mA of leakage current; when I use these I am happy if they are accurate to the nearest 0.1A.
A google search for leakage current sensor brings up many options; I have never used these and could not give you any advice as to which to pick. I looked at one and it's specs suggest that it has about 0.5mA of error measuring 5mA of leakage on the 40mA scale. https://www.calright.com/product/reed-st-9809-ac-leakage-current-tester/
Regarding your question about the output of the sense toroids in the GFCI, they have lots of turns in the sense coil (1000 in the schematic you posted), so the output current of the coil is a small fraction of the sensed current. This very small current is passed through a resistor (the 1.1 meg resistor in the schematic) to give a voltage which is easy to sense. In the schematic you gave, 4mA of leakage current would give a voltage of about 5V across Rsns.
-Jon
I would not trust a random clamp meter for general AC use designed to detect single mA of leakage current; when I use these I am happy if they are accurate to the nearest 0.1A.
A google search for leakage current sensor brings up many options; I have never used these and could not give you any advice as to which to pick. I looked at one and it's specs suggest that it has about 0.5mA of error measuring 5mA of leakage on the 40mA scale. https://www.calright.com/product/reed-st-9809-ac-leakage-current-tester/
Regarding your question about the output of the sense toroids in the GFCI, they have lots of turns in the sense coil (1000 in the schematic you posted), so the output current of the coil is a small fraction of the sensed current. This very small current is passed through a resistor (the 1.1 meg resistor in the schematic) to give a voltage which is easy to sense. In the schematic you gave, 4mA of leakage current would give a voltage of about 5V across Rsns.
-Jon