Gentlemen... finally, THE END!
This discussion has one goal: to make clear(er) why PFC, with its promise of loss reduction, did not materially alter power consumption as measured on the surface.
Consider an example:
A motor having a 100 kW power draw, and a 90% efficiency! The power-draw must satisfy three conditions: a) conversion to mechanical output (90% x 100 => 90kW); b) winding-loss (say 8% x 100 => 8kW): and c) core-loss (say 2% x 100 =>2kW)! Now include submersible-cable losses (say 8kW)! Thus, surface-measurement should show a 108kW power-draw from the power source, while down-hole the motor's power-draw is 100kW!
How are losses affected by voltage and current?
Theoretically, the power-conversion value is fixed; winding and cable-losses vary with the square of current; and core-losses vary with terminal voltage! Assume the PFC reduces current by 50%, resulting in a reduced cable V-drop! Down-hole, the motor's terminal voltage-rises 5%!
How are losses in the example affected?
Winding-loss is reduced (0.5² or 0.25 x 8 = 2kW), cable-loss is reduced (0.5² or 0.25 x 8 = 2kW), and core-loss is increased (1.05 x 2kW = 2.1kW). Theoretically, then, the surface-measurement should be (90kW+2kW+2kW+2.1kW) ~ 96kW !
Why, then (in PtonSparky’s case) did power-draw not decrease?
Instead, it increased a bit! The resultant improvement in the motor’s performance was a decrease in motor-slip, hence an increase in motor speed. Flow-rate, per The Affinity Law, increased in proportion to speed raised to some exponent! That exponent is between 2 and 3, depending on pump design. It follows then, that there is a corresponding increase in mechanical power requirement.
Regards, Phil