wrap the EGC 6-7 turns through a ferrite ring. @150MHz just a little choke and ferrite should make it look like a MΩ ckt and should bring amps down to zilch. try sticking the primary winding of a old xfrmer inline with EGC to see if the tripping stops.
Hello! I can't possibly tell you how much trouble I've been having with this issue. Two of my top 5 customers have moved to Siemens because of this issue, and I'm a Square D house.
Would you mind telling me what type of ferrite ring to use? I'm totally unfamiliar with that type of product, and I would love something to propose to my contractors so that they don't have to move their businesses. I've even brought the Square D rep down to talk to them, and they have no solution.
We're a square D house too and no suppliers In our region carry any Siemens. I get them from Zoro or a South Central Pools, a local pool supplier who matches the online price.Hello! I can't possibly tell you how much trouble I've been having with this issue. Two of my top 5 customers have moved to Siemens because of this issue, and I'm a Square D house.
Would you mind telling me what type of ferrite ring to use? I'm totally unfamiliar with that type of product, and I would love something to propose to my contractors so that they don't have to move their businesses. I've even brought the Square D rep down to talk to them, and they have no solution.
Btw, the Siemens engineers were not on board with using a ferrite. I still plan on trying them once i get the right situation.
Sent from my SM-G928V using Tapatalk
See attachment.
We wire alot of Pentair VSP. I have had several trip GE gfi's and regular seimans but get a "Pentair seimans" and see if that helps. They are more expensive but stops nuisance trips.
Yes, thats the "special" Pentair breaker.what is the model # of this special AFI/GFI ocpd. i will buy one and crack it open to see whats inside, my guess a tiny ferrite is in there.
is it this item
https://www.pentairpool.com/en/products/automation/gfci circuit breakers
???confused here but yes QPF is QPF.QPF is QPF, yes? 120 vs 220 QPF should be the same? Any manufacturing dates to be noted that would make a diff?
???confused here but yes QPF is QPF.
120 vs 220, I'm not sure if they're the same.
The Pentair version is only available in a 2 pole.
Well according to Pentair, the problem got worse after the self test was added but I cannot confirm this.
Sent from my SM-G928V using Tapatalk
Well according to Pentair, the problem got worse after the self test was added but I cannot confirm this.