Re: Pimp My Ride
The looks of my truck have nothing to do with my work. We are an obsessively clean shop. We do a total clean up each day. Our work is clean, neat and above code. Every day, I put all of my waste (wire scraps) into garbage bags an haul the waste back to the shops dumpsters. I am not a slob. Yes, my truck is a wreck.
BTW, the crane is fully operational despite of the rust.
Right now, we are installing a 4000 amp service for a winery. I am not yet involved with the project. Tonight, I heard discussion about using the crane for the overhead service drop. The controversy seems to be how we are going to hook up the fire pump ahead of the service. City water won't provide enough pressure to run the stand pipe. The city wants the winery to install
an underground storage tank to provide adequate water pressure in case of fire. The winery wants to use their olympic swimming pool as a water storage system for the fire pump. Poco won't let us tap the fire pump ahead of the meter. My boss is trying to figure out how to tap, for the fire pump, in between the meter and the main disconnect. Will the tap be fused? The AHJ can't decide. What size wire to tap with? It will have to be about twice locked rotor current for the pump. If there is a problem with the pump, it will have to burn without tripping an OCPD. These are the things our shop is negotiating. Whatever the outcome, I am the mechanic who will make it happen. Please do not judge me on the appearance of my truck. I do more than rope homes.
[ October 05, 2005, 10:58 PM: Message edited by: sparky_magoo ]