I agree that for normal people (Jim is far from normal ) the drops they supply do handle the loads. They use small wire to save on wire cost and can't blame them for trying. Sort of proves that nec often has us sizing our service too large. Why force me to install 200 amp service on my side if they supply only 100 amps.
Becuse they can supply much more than 100 amps via the drop.
NEC current ratings are meaningless to the power company.
One would think nec would not allow me to be fused higher than the supply wires.
They are not, you NEC riser is fused per the NEC I assume?
So after what happened here does it look like "The power company knows how to do the work on their side of the service point" ?
Yes, they know that the wires they used to supply your home are more than adequate to supply an NEC sized 200 amp service. You are exceeding NEC loading on that service.
Besides the fact that a bad termination can let go regardless of the loading on the conductors.
I have 200 amp service and need it all
A mustang does not need a 5.0 to drive in the city.
I bet if you did proper 220 load calcs based on the equipment in use that night the NEC would require more than 200 amps.