POCO finally believed me
I'm gonna sound like a broken record here but since none of y'all seem to be listening: :grin:
The damage Jim talks of and has shown in his pics DOES NOT fit the overloaded drop scenario! The fact that it is at pretty much regular one-foot intervals, coupled with the damage I highlighted in earlier post #38, screams defective/damaged insulation resulting in corrosion and hot spot failures.
If the drop was damaged from overload the ENTIRE length of insulation would have been melted/bubbled. I have seen this firsthand.
Another thing that doesn't fit with the overload theory: Unless the party lighting is full-on and static (very unlikely), every single A/C unit he has is running, every popcorn popper and crock pot was heating full tilt (only at startup of the party at worst), and his sound system was feeding a sustained signal of low frequency (the most power-hungry of audio spectra), the steady-state draw would not be sustained long enough to melt the drop, not without tripping the main.
I'm wiling to bet that Jim is about to go through a lot of unnecessary work and expense. :roll:
OK Mr. Microphone, take off the headphones and put down the record player.:grin:
I believe several of us have already said it is probably not the load as the #2 would normally handle the load. But I think it is a bit pre-mature to draw conclusions yet as we do not have the complete story. While it is a lesser probability, it might still be the load.
I agree.
My point at the beginning has been if he is overloading that conductor he is overloading his service. I doubt he is overloading either.
I disagree. I think Jim's load is close enough to unusual that he might could make a case for an under-sized drop.
Besides, satisfying our curiosity is worthy of Jim's time and expense.:grin:
I am not spending anything yet. Will be watching the balance of loads close. Hopefully it simply was defective wire. Note that only 1 leg had damage. I do think at best i hit a few peaks but still under 150 amps and even in Fl heat of 100 and no wind it should it should take the load. Time will tell.
Will monitor line volts Sat night because both legs are available at DJ booth.
Consider that the normal rating might not apply to your conditions. Given the right conditions, it would not handle the load.
For example:
Given the air temp of 100F and an XLP insulation rating of 90C you have an ampacity of 126 at zero wind and 129 at a 2ft/sec wind. With your unbalanced load, you could exceed this value.
Given the air temp of 100F and a current of 150 amps you have a steady-state temperature of 103.9C at zero wind and 103.6C at a 2ft/sec wind, both of which exceed the 90C insulation rating.
Some damage might been done last winter when i did trip the 200 amp breaker 2 times (not same night). Did remove 11 kw load by replacing electric heat in 1 area with propane. That seemed to be cure. We now are at our peak time of year when the AC is being worked hard.
At that time i did go over all of my connections and poco did same on there end. (we both had a few bad ones) At that time poco found a but splice where the #2 and 1/0 joined at the street had melted the insulation. And guess what ,same connection again melted the insulation of that splice even after it was changed.
This week will be keeping sharp eye on voltage and will have my amp probe ready and a ladder next to pole. I will check at the weather head.
Maybe i am wrong but when wire melts before a breaker trips it usually means 1 of 2 things, breaker bad (not likely it is SQ D ) or the wire is undersized. I might need to go to the PSC to get results.
Added to this mistry is how a 50 kw transformer can handle 8 customers. Pointed all this out to engineering and suggested they take me from transformer on other side that is 80 feet shorter ,but what does an electrician know.
They been warned many times and i am tired of them.
It just depends on the calcs. The diversity is a big player.
I have one table showing eight 1500 sq ft, total electric homes having a diversified demand of 57.5 kW which is within the overload range of the transformer. A different table shows a 50.2 kVA summer load and a 68.3 kVA winter load for eight 1500 square ft homes, which also falls within the overload ranges.
But, as you can see, these could be considered marginal. Some areas would have higher load profiles, some lower. I'm sure that the local POCO has tables that match the typical loads for your area.
The monkey in the wrench is what happens when you have non-typical loads. Maybe the POCO has looked at the bills for the eight customers to check the loading, maybe they haven't.
Either way, the kVA capability might be fine but I find it hard to believe the voltage drop calc is fine.
Problem is the bills would not show anything but averages over a month and that would never see my load for 6 hours of way over average each Saturday night.
What i hope to catch on Saturday is a voltage drop that puts them at fault. Then i can apply presure on them. Seems like a shame that they would rather see a transformer blow up or a line melt before taking action.
I should not even need to be dealing with this problem.
Just how does one manage to get a full 200 amps ? Put in 320/400 amp service to maybe get full 200 ? That is flat out crazy when all that is needed is a drop of correct size.
Problem is far from being over. I am doing my part in trying to keep loads down.
Tell the POCO you are adding load and fill out a new load calc sheet, maybe over estimate the load a little. I have to admit I am impressed that you were able to twice trip a 200 amp main. That is not common in a normal size house.
I don't know about your POCO, but the last house I put a 320/400 main service on (underground fed) the POCO put 350 AL. Seems small to me.
Time to put this dead horse down...
For example:
All well and good BUT it would STILL take a sustained load to cause damage to the conductor (why do you think the NEC spells out 3 hours as a continuous load? :roll: ) to compromise the conductor and the "spot damage" that Jim experienced does NOT fit an overloaded conductor's damage pattern.
To take the bold points in order:
1:Yes it is possible that the spots developed or started when the breaker tripped, but again if the overload was sustained enough to damage the conductor the ENTIRE LENGTH would have been damaged.
2: Same connection melting says the guy who did it, did it WRONG. Probably did not clean the al adequately or didn't crimp it tight. Means nothing in the context of this issue at hand.
3: Good idea in theory but meaningless in practice. If your meter can capture peaks and plot them in relation to total time, it would be valuable. (Think data recorder) otherwise all you're gonna see is the fluctuating load as the lights flash and the music thumps. :grin: If you read any long-term reading under 200-220 amps on any leg you're NOT gonna hurt the drop. (3-hour rule.) Do you feel like living on the ladder for three hours to get those readings? And ANY sag below the threshold for anything more than a few minutes would take you out of the continuous load definition.
4: Read what the others have said about transformer loading!!
mivey in post #47 said:
20 kW in winter or summer? For how long of a period? That 50 kVA can handle 150 kVA for brief spurts, and may start routinely peaking at 70 kVA before even being considered for a change-out:
Per-unit overloading for normal transformer life:
Over-load Hrs: per-unit for 50%, 70%, 90% pre-loading
0.5 hrs: 1.89, 1.77, 1.59 pu
1.0 hrs: 1.60, 1.54, 1.40 pu
2.0 hrs: 1.37, 1.33, 1.24 pu
4.0 hrs: 1.19, 1.17, 1.12 pu
8.0 hrs: 1.08, 1.08, 1.06 pu
Even if pre-loaded to 50 kVA then over-loaded to 77 kVA for an hour, you only lose 0.10% of the transformer life. Don't forget that some of your 20 kVA of load is cycling on and off also. The older transformers seem to be a lot tougher too.
The POCO DOES NOT follow the NEC rules on transformer loading, they base it on overload capability of oil-cooled transformers, loss-of-life vs. overload tables, and their own experiences on "burnout rates" to determine if a transformer is undersized. Prior to a burnout the ONLY thing that will motivate a POCO to change to a larger transformer is if the customer is experiencing very low service voltage. That is why they are not listening to what you have to say about it. Unless you can PROVE that you are experiencing long-term voltage issues (and I doubt your parties would be considered as "long-term") they are NOT gonna move you over..unless YOU are willing to pay for it. Heck, if you're willing to throw down several thousand dollars they will happily install your very own dedicated transformer...with a catch. If you blow it up, YOU will pay for its replacement. (It is considered in this case to be "customer-owned".)
Exactly, diversity is how the POCOs figure out loadings on transformers.
As for the voltage drop issue, I haven't seen anything Jim has said that indicates a voltage drop issue, which also backs up that the drop is NOT undersized as if it were he would have SUSTAINED, LONG TERM voltage drop issues. He would need a data recorder at his meter location to prove it.
Jim, again a voltage drop on during your parties WILL NOT motivate them to change anything!! First off, it is what they would consider a SHORT-TERM condition, second it is unusual for a residential customer to have such high demand on a regular basis, third if you push the POCO too hard they WILL push back and you may suddenly find your parties getting a LOT of attention from City code enforcement and/or the fire marshal, and finally they can tell you if your parties are causing such a drop, then YOU would be required to upgrade your service (and pay the POCO for an upgraded drop and/or transformer.)
Have you even tried out the new drop arrangement? If the voltage stays within tolerance (and remember POCO looks at long term, NOT sags from the lighting or music) then the POCO will consider the matter closed. If the drop fails again it is THEIR problem, not yours.
Finally, the smartest thing you've said so far is "I am doing my part in trying to keep loads down."
Are you really willing to go through all this expense and hassle?
couple more swift kicks first
All well and good but the 3 hours is not relevant to this drop. The emergency overload rating for the XLP is 130C and for that size wire and configuration it will reach that temperature long before even an hour is up, maybe more like 30 minutes.
Also, I thought you spoke of bubbled up insulation in one foot increments?
One foot increments or just a couple of isolated spots? One of the pics Jim posted was of a melted wire. No way did the load cause the wire to melt unless enough of it was corroded away to leave minimal strands so that falls in line with the corrosion angle (water from weather head?)
Connections are a weak point and would be a likely failure point for overloads. Can't imagine the load got high enough to fail a good connection.
Based on what information? There is no 3-hour rule. Plus, a 200 amp load could very well hurt the insulation as it would push it way beyond the 130C mark given the right ambient conditions.
Do the math. It is very easy to get an unacceptable voltage drop calculation.
What expense? Moving some load? Metering some loads?
What hassle? This is what he does for a living. He might actualy enjoy the adventure.