Feeling stupid this morning...
Is there an NEC requirement for a pull box every 200' of conduit?
(A little background, I have an engineer who insisted that it is in the NEC but can not give me a reference and I cant find one either.)
The most likely reference would be ANSI/TIA/EIA-569, 4.4.2.1: "No section of conduit shall be longer than 30m (100ft) or contain more than two 90 degree bends between pull points or pull boxes."
But, no, there is no NEC requirement for distance.