wardwire said:Is it necessary to pull a grounding conductor through e.m.t. conduit when set screw fitting are used . I have always just bonded my boxes and not pulled a grounding conductor . Is this still o.k.?
Thanks , greg
petersonra said:generally yes. emt is a legal egc.
That would be a code violation. If you install an EGC of the wire type, even in a metal raceway that is itself suitable for use as and EGC, the wire must be sized per 250.122. That would require a #12 EGC for a circuit with #12 conductors.Typically, we pull one size of wire down in grounding conductor than the main conductors we pull through the pipe (#12 wire, #14 ground).
Standard operating procedure here... I don't think I've ever bought a roll of #12 green.don_resqcapt19 said:AltonToth,
Don
Don
electricalperson said:i always run an EGC with emt. i dont trust the set screws too much
My cell phone has never rung while I'm running EMT.:grin:Dennis Alwon said:It is very easy to get distracted and forget to tighten one every now and then.
Dennis Alwon said:I am sure you know this but It's not the set screws that you can't trust it is the installers that don't tighten them. It is very easy to get distracted and forget to tighten one every now and then.
tryinghard said:shorts wont open a breaker, I've seen this many, many times!
chris kennedy said:I'm on the record many times here stating I always install an EGC (full size) in EMT.
electricalperson said:thats pretty much the reasonwhy i run an EGC just incase someone forgot to tighten down the screw or locknut in a box
iwire said:I find this to be one of those issues that electricians do just so they can say they are better then those that don't.
wireman71 said:I've seen a lot of conduit pulled apart. Set screws not tightened. Lock nuts not tight. Unless it's a steel building with steel studs I'd run a ground.