K8MHZ
- Electrician
Never mind.
Never mind.
the page-1 i was talking about was literally the 1st page past the cover page of nec 2014. all your local law says is, that the AHJ will use the NEC book as the reference.
there is no jurisdiction from NFPA to the AHJ, as they duly note on page-1.
its the chosen reference by which the AHJ can interpret any way they like as they have the right to do so.
That is incorrect for MA, RI and CT. It is adopted into the regulations here in MA.
Correct as a private non-profit (The NFPA) has no authority at all to create a law.
The bold part is a falsehood, plain and simple.
The AHJs interpretations must have a basis in the code. They cannot interpret 'shall be permitted' to 'shall not be permitted'.
FL Building Code 2010, chap 27 2701.1, adopts NEC as the reference for the whole state.
the part in red box however is not mandated to be there, FL can put whatever they want there, could be "State of FL Electric Code 2014.1A" if they want.
by law, they require something to be there, adoption of something is required by law, the "NEC" part has nothing to do with the law.
next is AHJ interpretation. it is then up to each AHJ to interpret whatever (cats, dogs, fur, NEC) has been adopted as the reference. AHJ's across the state may have varying interpretations of the broad & vague NEC code, etc. for the most part, most AHJ's will have same interpretations, gray areas leave it open to each AHJ to do with it what they want.
The term 'shall' makes the rest of the sentence mandatory, not optional.
true. which means no matter where in the state you may be, whatever is placed into that red box is it, no exceptions. FL constitution does not say that red box must be "NEC". you see the diff now?
You do realize that NFPA 70 IS the NEC, don't you????
???This is NOT where Florida adopts the NEC as part of the building code. See section 553.73 et seq of Florida for the actual enabling legislation. And by the way, they can't just put "anything" there. See the enabling legislation.
i provided the verbiage from FL building code.[SIZE=-1]“Approved” means conforming to the requirements of the Florida Building Code.[/SIZE]
just 70??? what about 70A, 70B, and 70E. those are not NEC ??
Only NFPA 70 is the NEC. The others are not. Here are the titles of all four books.
NFPA 70: National Electrical Code®
NFPA 70A: National Electrical Code® Requirements for One- and Two-Family Dwellings
NFPA 70B: Recommended Practice for Electrical Equipment Maintenance
NFPA 70E: Standard for Electrical Safety in the Workplace®
Your question marks don't make sense. If you followed the link, you would have seen that's where the various codes are actually adopted, not in the Florida edition of the building code. The Florida edition of the building code is the end product of the legislation.
my highlight-copy went to far, my bad.
70A is an addon to 70, so i find it as being part of the NEC code stuff since its not in 70.