Ok... so it is a branch so that technically I could roll up, and instead of hooking an rv to it, hook up my shop equipment or cookstove..lol... no problem.. will call it such from now on.
Idaho is on 2017 statewide. This question apparently came up and was addressed.
https://dbs.idaho.gov/programs/electrical/publications/Electrical_Newsletter_7-2017.pdf
They agree with my opinion that if the intent was to require GFCI
on 30 and 50 amp receptacles, 551.71(F) would have included this. The paragraph modifies 210.8(B) in their opinion.
I'd be interested to find any other state opinions for or against.
Most of these articles mention "RV Park" Receptacles.
To me, the language still needs to be improved.
Not all RV receptacle outlets are installed in "RV Parks".
It would be best to refer to the RV Outlet itself, not a particular geographical area such as an "RV Park" if the rule doesn't apply to 30 and 50 amp outlets for RV's.
JMHO.
Jap>
If I install a 30 or 50 amp RV outlet somewhere other than an "RV Park", do I still have to GFI Protect it?
JAP>
It shouldn't be this difficult or unclear.
AHJ is certainly allowed to set their preference on something like this that isn't all that clear in the NEC. But IMO 551 does not mention anything except the 20 amp receptacles when it comes to GFCI protection, how does having "nothing" in 551 modify something from chapters 1-4?Idaho is on 2017 statewide. This question apparently came up and was addressed.
https://dbs.idaho.gov/programs/electrical/publications/Electrical_Newsletter_7-2017.pdf
They agree with my opinion that if the intent was to require GFCI
on 30 and 50 amp receptacles, 551.71(F) would have included this. The paragraph modifies 210.8(B) in their opinion.
I'd be interested to find any other state opinions for or against.
Per wording in 2017 - at a dwelling no, anyplace else and assuming outdoors, yes.If I install a 30 or 50 amp RV outlet somewhere other than an "RV Park", do I still have to GFI Protect it?
JAP>
AHJ is certainly allowed to set their preference on something like this that isn't all that clear in the NEC. But IMO 551 does not mention anything except the 20 amp receptacles when it comes to GFCI protection, how does having "nothing" in 551 modify something from chapters 1-4?
Per wording in 2017 - at a dwelling no, anyplace else and assuming outdoors, yes.
Plug your 50 amp RV in at home and you won't experience shock hazards. Plug it in anywhere else and apparently you are subject to shock hazards![]()
AHJ is certainly allowed to set their preference on something like this that isn't all that clear in the NEC. But IMO 551 does not mention anything except the 20 amp receptacles when it comes to GFCI protection, how does having "nothing" in 551 modify something from chapters 1-4?
I'm more likely to get electrocuted at home than I am at the camp site.
That's where I wash my fifth wheel and do all the other maintenance on it.
I would think the biggest shock hazard at the site would be when you go to unplug it from the pedestal.
One tends to palm the male cap and your fingers wrap around and come close to the stabs as your working it out.
.
The newer rv male caps have a handles molded onto the back that you grab onto making this much less of an issue.
Jap>
Just shut off the receptacle.
GFCI protection on RV receptacles is a rather odd requirement. They *are* functionally feeders, just with plugs.
Not all Power outlets have the breaker in the outlet itself.
JAP>