currentelectric
Member
- Location
- colts neck new jersey
Can you please clarify the purpose and intent of article 445.13/ ampacity of conductors. Is it ok to use a 4 conductor #2 SER aluminum cable for a feeder to a service entrance rated transfer switch from a 20 KW kohler RESAL generator which comes supplied with a 2 pole 100 amp breaker. The nameplate rating for this generator for natural gas is 75 amps. According to 445.13 115% of 75 amps is 86.25 amps. Since # 2 SER has a rating 90 amps is adequate for my application. Out of over 100 installations we have completed in the State of New Jersey with the Kohler 20 KW generator I have never had a problem passing electrical inspection. Unfortunately I have had one issue with an electrical inspector who has failed my installation because of the use of the # 2 SER wire from the generator to the transfer switch. I have provided him with a total load calculation for this particular house with the use of a Kohler Load Controll module which sheds 2 AC loads, 30 amp 240 volt oven, and a 30 amp hot water heater. The inherent design of the generator and the use of the load control module prevents and loads above 75 amps. Also does the exception in this article also dictate that the rating of the wire can be rated for 75 amps? Ralph Somma , Current Electric Of Colts Neck LLC.