jxofaltrds
Retired ESI
- Mike P. Columbus Ohio
- Creator
Yeah, it's not all that important, but I really don't like inaccuracies on the Internet. Flog me with 48-channel snake fanout. :lol:
Don't tempt these guys!
There was a company called ECOS that made a high quality tester for single phase and three phase wiring in the 90's.
Not sure if they are still in business, but I have a couple of their instruments. Their three lamp tester was about $100.00
You can find anything on eBay if you look around: http://www.ebay.com/itm/NIB-USA-ECO...349?pt=LH_DefaultDomain_0&hash=item4cf97af8bd
However, while is does appear to do a lot more tests than a standard 3-light "ice-cube" tester, it doesn't perform as many functions as a modern Ground Loop Impedance Tester (GLIT) such as a Amprobe INSP-3 or Ideal SureTest. Also, unless I'm missing something entirely, it won't indicate if a Bootleg Ground Outlet is wired with "correct" or "reverse polarity". And none of these GLIT's (old or new) will tell you if somebody daisy-chained a new outlet onto a RPBG outlet with at least 15 feet of 12 gauge wire. All GLIT's will report no errors in that case, even though the ground and neutral could be sitting at 120 volts above earth potential.
In modern buildings that should never be an issue, but in renovations where extra outlets need to be added to meet code, this is a real possibility. That's why you need to establish a known-good earth reference to test all renovated outlets for hot grounds. Unless you've wired and inspected it all yourself, you just don't KNOW what some DIY "electrician" did 30 or more years ago.![]()
61040 NEON CIRCUIT TESTER
using a neon two lead tester has been used for years to detect which wire is hot, even that PDF about GFCI's I posted made this statment and told how to do it, by holding one of the neon's test lead and touching the other to the wire or contact of the device, if it glows its hot, if not its neutral or ground.
Yeah, I used to do that myself a long time ago, but in retrospect it seemed like a bad idea. I've even seen the posting of using a neon tester for this purpose "removed" from this forum at least once (if memory serves). I guess if the neon tester has a 100K limiting resistor, the max current that could go through you with 120 volts would be around 1 mA or so, way beneath any shock danger level.
What's the "official" NEC or OSHA spin on using a neon tester like this? Dangerous? Not dangerous? Just a bad idea? What?![]()
Jim Brown suggests using:
One of the most problematic wiring errors, and also the most difficult to detect, is the
exchange of Neutral and Equipment Ground (PE). This error causes the full load current
to flow on the Equipment Ground rather than the Neutral. This establishes a current
loop with a very large loop area, which can result in very strong magnetic coupling of
hum and buzz into signal circuits. A magnetic field probe may be the most effective
way to expose this sort of error.
Power and Grounding For Audio and Audio/Video Systems -- A White Paper for the Real World
http://www.audiosystemsgroup.com/SurgeXPowerGround.pdf