wwhitney
- Berkeley, CA
- Retired
The closest I found was 110.4 which includes the sentence "The voltage rating of electrical equipment shall not be less than the nominal voltage of a circuit to which it is connected." That references "nominal voltage" rather than "voltage to ground." So are 300V conductors OK to use on 480Y/277 (the nominal voltage) because the voltage to ground is less than 300V?I just extended that by assuming that the insulation for a conductor must be rated equal to or higher than the voltage to ground of that conductor.
As a practical matter, how does the voltage rating of insulation depend on insulation thickness? E.g. if the insulation thickness is doubled, does the voltage rating double? If so, then 300V conductors should be OK to use on 480Y/277.
Cheers, Wayne