They aren’t rods at each joint. I’ve pinched an idea off the DNO’s, an earth tape from the cable armouring buried alongside the joint.
A true PME system not to be confused with CNE which you use.
What I’m doing falls outside the scope of BS7671, it comes under BS7430-2011-COP.
Terminating the cable is no different to normal SWA except the length of the tails need to be longer and dressing the cores so they don’t have sharp kinks (corona discharge). The UG joint boxes are just large sized ScotchCast kits but I won’t use mechanical connectors, I’ll solder them with a ferule.
This job is designed to outlast me (that’s not a very good guarantee)
A true PME system not to be confused with CNE which you use.
What I’m doing falls outside the scope of BS7671, it comes under BS7430-2011-COP.
Terminating the cable is no different to normal SWA except the length of the tails need to be longer and dressing the cores so they don’t have sharp kinks (corona discharge). The UG joint boxes are just large sized ScotchCast kits but I won’t use mechanical connectors, I’ll solder them with a ferule.