It’s a GFCI just like the outlet. It’s going to trip at the same time the outlet would or it’s not doing it’s job.Dual function cb?
It’s a GFCI just like the outlet. It’s going to trip at the same time the outlet would or it’s not doing it’s job.Dual function cb?
Larry here’s the big question - Does this only need to happen when you initially plug it in or is this going to happen every time the fridge is above temp and kicks in to cool down?I'll take a stab at it:
Get the refrigerator running and cooled to normal temperature on a non-GFCI-protected circuit first.
Don't ask me; I was just translating.Larry here’s the big question - Does this only need to happen when you initially plug it in or is this going to happen every time the fridge is above temp and kicks in to cool down?
Don't ask me; I was just translating.
I took it to mean that the refrigerator would run differently after the initial cool-down.
Others who chimed in suggested that residual moisture would be driven out with heat.
Nice find. This UL 60601-1 compliant device appears more effective than isolated grounding for sensitive medical equipment.Using an approved external isolation transformer like this one, for example (or perhaps a more economic model): https://www.amazon.com/Tripp-Lite-IS1800HG-Isolation-Transformer/dp/B00008N6S7
The transformer could still be grounded and it is not installed as part of the building. Perhaps it could be placed 6' away from the sink to skirt that, if it applies to the appliance. Please let me know your take on this if I am mistaken - from the perspective of liability to the electrician, he has not made any installation against code this way, as his job stopped at the receptacle. It is up to the end user to operate the transformer, like any other appliance.
The receptacle is within 6 feet of the sink but would it even matter if the refrigerator is within 3 feet of the sink and not GFCI protected? I would think that a big metal item so close to the sink should be GFCI protected even if the receptacle is in the front yard.
The 2013 revision of UL 499, for "Leakage Current" p28 of 36 prohibits leakage current above 0.75mA, except during heat up & cool down when the "Standard for Leakage Current for Appliances, UL 101" allows up to 2.5mA. Both standards are well below, or compatible with Class A GFCI of 4-6mA.The lower speed might then shift some of the common mode noise to lower frequencies which can pass through the low pass filtering of the GFCI detection circuitry and cause it to trip.
It will survive a drop test.Nice find. This UL 60601-1 compliant device appears more effective than isolated grounding for sensitive medical equipment.
When Brick & Mortar OEM's like Tripp Lite use Amazon.com, its amazing to see that inventory with product listings, such as UL 60601.
That probably goes away once OEM learns to register the store at an overseas address.
Samsung inverter refrigerator encountered last month also caused severe shock, only when touched at specific point.1) Manufacturers not getting on board and designing their hardware from the get-go to not trip a GFCI when properly functioning.
Roger that.a big metal item so close to the sink should be GFCI protected even if the receptacle is in the front yard.
That solution for not using GFCI went away way back in either 2005 or 2008 NEC.Where is the recept? Behind the fridge? What happend to the single plex solution?
Actually an open EG likely will eliminate high frequency leakage that is tripping the GFCI. I've run into this with clothes washers with variable speed motors. Plug them into a two to three prong cheater and they run fine. Plug them directly so the EGC connects and they start the cycle fine - fill the machine with water but the instant the motor is called to run they trip the GFCI. If they would just electrically isolate the motor from the frame of the machine that usually resolves the issue.I wondered too. A good EG is all that may be required.
That from a guy, me, who had a GFCI ahead of a chest freezer because it's next to a utility room sink where I used to wash the legs and feet of grandchildren while they sat on it.
The reality that the NEC threw out the window many code cycles ago is the importance of a good equipment grounding conductor. GFCI is supposed to be there to kick in should the EGC become compromised. Now they want GFCI on so many things with the justification of "because we can".The receptacle is within 6 feet of the sink but would it even matter if the refrigerator is within 3 feet of the sink and not GFCI protected? I would think that a big metal item so close to the sink should be GFCI protected even if the receptacle is in the front yard.
Residual moisture is about the only thing that suggestion will work for. If it is tripping because of high frequency leakage of a variable speed compressor it is not going to matter. So I guess it won't hurt to try it for a while on non GFCI protected circuit to see if it will dry something out. But after that, something else is an issue.Don't ask me; I was just translating.
I took it to mean that the refrigerator would run differently after the initial cool-down.
Others who chimed in suggested that residual moisture would be driven out with heat.
Might been possible then. GFCI manufacturers that have a lot of $$ to throw at convincing the CMP's however will not let this happen very easily.Back when GFCIs were first required for commercial kitchen receptacles, I wondered if it would be possible to have a combination GFCI / assured EGC system, where the GFCI thresholds would be raised if the EGC tested intact.
Jon
Exactly, but the product standards did not even address leakage current for hard wired equipment, because the product standard assumed that the code required equipment grounding conductor will do its job. The expansion of GFCI into hard wired equipment and the energy standards that require the use of power conversion equipment have resulted in these issues....60 hertz leakage current because the product standards for hard wired equipment did not address that issue, and the high frequency current that results from the power conversion equipment. To separate issues that require action in the product standards before the issues will be resolved.The reality that the NEC threw out the window many code cycles ago is the importance of a good equipment grounding conductor. GFCI is supposed to be there to kick in should the EGC become compromised. Now they want GFCI on so many things with the justification of "because we can".
The special purpose GFCIs require a ground check conductor. If the SPGFCI can not verify the equipment grounding conductor, the device opens the circuit, even without any leakage current.Back when GFCIs were first required for commercial kitchen receptacles, I wondered if it would be possible to have a combination GFCI / assured EGC system, where the GFCI thresholds would be raised if the EGC tested intact.
Jon