winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
The special purpose GFCIs require a ground check conductor. If the SPGFCI can not verify the equipment grounding conductor, the device opens the circuit, even without any leakage current.
Well that is simpler logic than I was speculating about.
Given that SPGFCI is already in the code for industrial applications, I wonder if it would be less of a push to get it as an exception for general 120V applications.
In other words keep the requirements for general purpose 5 mA class A GFCIs, but add an exception which permits SPGFCI type approaches for plugged in stationary equipment such as appliances with VFDs.
I bet that in actual practice, 100mA leakage threshold, combined with assured EGC would provide better safety than a 5mA leakage threshold.
Jon