Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
But that is not what the code is requiring related to the kitchen or the exterior outlets, it is requiring the 4-6mA for personal protection.Agreed that the 20mA threshold is not as safe as the 4-6mA class A protection.
But the combination of 20mA protection with enforced EGC connection changes this balance. 20mA through a person is a significant hazard. 20mA through the EGC not so much.
Remember that we are talking about equipment fastened in place, where the danger is that the EGC fails, and a separate failure energizes the chassis.
Jon
The only times code references SPGFCI use is related to 680 and 410.