Agreed on how GFCIs function.The GFCI isn't measuring current on the EGC, but rather net current on the supply lines. Of course any capacitive leakage is ending up on the EGC or another path back to the transformer.
So I take your point to be that the idea of putting the ferrite core on the EGC will only work when the EGC is the only return path for leakage current. Which I was assuming, but I guess is sometimes not true. E.g. if the refrigerator happens to have internal metal water piping and has a metal water supply (pretty rare these days, I think), then that would be another path for leakage current, since the metal water supply system will be bonded, creating a ground loop.
Cheers, Wayne