Then whats the relevance of the comment :I was referring to an across-the-line motor. No VFD
What rectifier stage?No different here except the rectifier stage prevents overcorrection.
Then whats the relevance of the comment :I was referring to an across-the-line motor. No VFD
What rectifier stage?No different here except the rectifier stage prevents overcorrection.
Across-the-line motor PFC capacitor compared to VFD DC bus filter cap. Latter has a rectifier stage ahead of it, former does not.Then whats the relevance of the comment :
What rectifier stage?
Two quite different scenarios. \You can't conflate them.Across-the-line motor PFC capacitor compared to VFD DC bus filter cap. Latter has a rectifier stage ahead of it, former does not.
Unlike PFC, unidirectional current flow. DC if you wish.If the caps are not 'visible' to the ac supply how are they charged?
I'm not conflating them. Just comparing characteristics, function, performance. Though you may not concede to the idea, they do have some crossover in these areas.Two quite different scenarios. \You can't conflate them.
The main purposes are different, yes. But a capacitor is going to perform as a capacitor no matter what its general purpose is, and that is the part which you do not want to concede. You are even saying the proper words to prove it: "...it doesn't return its energy to the supply."Unlike PFC, unidirectional current flow. DC if you wish.
And, unlike PFC, it doesn't return its energy to the supply.
They serve two totally different functions.
NoUnlike PFC, unidirectional current flow. DC if you wish.
And, unlike PFC, it doesn't return its energy to the supply.
They serve two totally different functions.
it doesn'tWhere does it say bigger is better in these articles? Please keep in mind I'm no VFD design expert so be precise please.
The DC cap bank doesn't - at least to seem to understand that bit. It justn't do what PFC does with a direct across the line motor. That's what you and Ing can't seem to, don't want to grasp.The main purposes are different, yes. But a capacitor is going to perform as a capacitor no matter what its general purpose is, and that is the part which you do not want to concede. You are even saying the proper words to prove it: "...it doesn't return its energy to the supply."
Helps if you are........it doesn't
basic understanding does
No need to be a vfd expert
The DC cap bank doesn't - at least to seem to understand that bit. It justn't do what PFC does with a direct across the line motor. That's what you and Ing can't seem to, don't want to grasp.
Let me ask you both a question. You have a dozen VFDs on a process line, powers from 100kW to 400kW. They are all fed from a common DC buss. How does altering the VFD capacitor bank affect the power factor in such a case? Can you at least begin so see the disparity?
Ing posted a link (#post#249 I think) from a VFD manufacturer. It has errors about power factor correction - clearly not written by someone with design level understanding. The trouble is that such disinformation is accepted as the gospel truth by some. And that saddens me.
"The moving finger writes........"
know any?Helps if you are........
But I'm not saying it does it in the same way. If the power factor of a VFD input is better than the same motor connected across the line at the same speed and loading there has to be a reason. And that reason is the DC bus filter cap(s). There are no active components in existence that I'm aware of that can improve the power factor of a motor. A passive component or second power source has to be involved. However you want to explain that is up to you.The DC cap bank doesn't - at least to seem to understand that bit. It justn't do what PFC does with a direct across the line motor. That's what you and Ing can't seem to, don't want to grasp.
We are talking power factor comparison motor vs. VFD input. Not just the input.Let me ask you both a question. You have a dozen VFDs on a process line, powers from 100kW to 400kW. They are all fed from a common DC buss. How does altering the VFD capacitor bank affect the power factor in such a case? Can you at least begin so see the disparity?
How so on a DC supply?as far as your multiple motor example
Net pf imrovement
...
if valid sources are dismissed there is no point
How so on a DC supply?
You wouldn't measure anything. The PWM drive wouldn't work.But I'm not saying it does it in the same way. If the power factor of a VFD input is better than the same motor connected across the line at the same speed and loading there has to be a reason. And that reason is the DC bus filter cap(s). There are no active components in existence that I'm aware of that can improve the power factor of a motor. A passive component or second power source has to be involved. However you want to explain that is up to you.
We are talking power factor comparison motor vs. VFD input. Not just the input.
If you completely remove the capacitor bank, will you measure a better or worse power factor at the AC source?
Yes.5 articles/papers/app notes, maybe more?
all from major mfgs; hitachi, ab, abb, etc
all saying that a vfd will improve pf due to the caps
all wrong