Knox
- montgomery, mn 56069
I AM IN THE PLANNING STAGE OF A GRAIN SETUP FOR A FARMER.
I AM WORKING ON SIZING THE SERVICE AND WOULD LIKE SOME SECOND OPINIONS.
HE CURRENTLY HAS A 208/120 3PH 600A SERVICE ON SITE. THE NEW SETUP WILL
CONTAIN THE FOLLOWING MOTOR LOADS THAT COULD POTENTIALY ALL BE RUNNING AT THE SAME TIME.
DRY GRAIN LEG: 1 - 75HP 3PH FLC 211A
WET GRAIN LEG: 1 - 30HP 3PH FLC 88A
LOAD CONVEYOR #1: 1 - 20HP 3PH FLC 59.4A
LOAD CONVEYOR #2: 1 - 20HP 3PH FLC 59.4A
DRYER BLOWER FAN #1: 1 - 20HP 3PH FLC 59.4
DRYER BLOWER FAN #2: 1 - 20HP 3PH FLC 59.4
DRYER BLOWER FAN #3: 1 - 20HP 3PH FLC 59.4
DRYER UNLOAD AUGER: 1 - 7 1/2HP 3PH FLC 24.2A
BIN FAN #1: 1 - 10HP 3PH FLC 30.8
BIN FAN #2: 1 - 7 1/2HP 3PH FLC 24.2A
BIN FAN #3: 1 - 7 1/2HP 3PH FLC 24.2A
BIN FAN #4: 1 - 7 1/2HP 3PH FLC 24.2A
CALCULATED FEEDERS USING (LARGEST MOTOR FLC X 1.25 + SUM OF REMAINING MOTOR LOADS FLC'S)
211 X 1.25 + 512.6 = 776.35
SIZE A MINIMUM OF AN 800A 3PH 208/120 SERVICE
I WILL MORE THAN LIKELY SIZE THE SERVICE TO 1,000A TO ALLOW FOR FUTURE EXPANSION AS THERE ARE ALREADY TALKS OF ADDING ANOTHER BIN OR 2 IN THE FUTURE AND MAY ALSO BE INSTALLING MOTORIZED SPREADERS AT THE TOP OF THEM.
AM I SIZING THIS CORRECTLY OR AM I MISSING SOMETHING.