It looks like the coil is missing, if I’m not mistaken, the coil voltage appears in that window between the terminals.
It looks like the coil is missing, if I’m not mistaken, the coil voltage appears in that window between the terminals.
Found a 360 view online, didn’t see a coil voltage anywhere. I wouldn’t think they would ship without a coil, but GE does ship the Spectra breakers without a rating plug, and since ABB is part of GE now, I wouldn’t doubt it! LOL!It looks like the coil is missing, if I’m not mistaken, the coil voltage appears in that window between the terminals.
From the looks of that intermatic timer clock I'd wage thats exactly what that does, The ICE cube relay was probably switching the neutral hence only 4 wires to the relay.is it not a problem that the original switch was pulse on or off (with intermatic controlling that) but now using a standard contactor that needs a constant coil voltage? seems like you need a new timer control that feeds On 120v signal during night and Off no 120v during day.
If that was the case, the cube relay would not have been needed. Old Kmarts used those pulse time clocks, much larger than that one. They used two programmable outputs, one for latch, the other for unlatch.is it not a problem that the original switch was pulse on or off (with intermatic controlling that) but now using a standard contactor that needs a constant coil voltage? seems like you need a new timer control that feeds On 120v signal during night and Off no 120v during day.
I am just saying that the clearing contacts are an option, not integral with the contactor. In your area, or dealing with your company, maybe your supply house are smart enough to automatically include that option when supplying to you, but you can get those contactors without the accessory. I am not trying to "win" and argument, but pointing out that novices must be aware of the component so they don't have the same issues that the OP did.The only ones I have used in the past 35 years that didn’t have clearing contacts, was the one I pictured. I have used GE, Square D, Siemens and ASCO. ASCO has a model that looks like a heat sink with a coil in the center. Siemens, GE and Square D all put their name on it. Those have a single coil.
no disrespect intended, but how do you know the old contactor was bad, if you are unsure of how it was supposed to run in the first place?
is it possible that there was simply an input issue to the old contactor controls, and that was why it stopped operating correctly? or was there some other tell that led you to believe the contactor needed to be replaced?

Probably the mechanism was getting worn, and the clearing contacts were not making/breaking like they should. I’ve had them bind up, and not open and close like they should because of the grease drying up. One contact opens, but the travel stops too soon, and doesn’t close the interock. Get that a lot on transferswitches that work on the same principle.I inherited this shopping complex from a previous electrician. I got the call that lights were out. The previous electrician told me that they have been having problems with the contactor for years, and he has to go and “wiggle”’it and manually switch it off and on to get it to work.
I reset everything, set the timer to turn on, couple times it wouldn’t switch, sometimes it would, and one time the contactor let out a fair amount of magic smoke while trying to close.
I replaced the contactor and relamped the entire parking lot with LED bypass and removed the mercury vapor lights.
As of this morning it’s all working as it should.