What about 210.11 (A)?
What about it?
Minimum amount of circuits needed for the calculated load.
Zip about adding up receptacles.
Do you add up breakers to calculate the load on a panel?
What about 210.11 (A)?
I totally know what you meant and that you were not being flippant on the subject.
It is just that I am way too sensitive to how it is used in casual conversation.
I get more upset than I should, but I am a historian at heart.
So, do not take my over blown out burst to heart.
I know you are a good man Charlie Brown.
210.11 is all about number of branch circuits needed, not about a max number of recpts that can be on a circuit.What about 210.11 (A)?
Doesn't it say ".....as calculated in 220"?
History was one of my worst subjects in school.....
This whole argument would be easily solved if the CMP read Charlie’s Rule and changed the wording properly to reflect their intent.
The whole argument would be easily solved it the hand wringers would catch on to the fact that a recept with nothing plugged into it is not going to overload a circuit and stop worrying about a max number of recepts on one circuit.
Ok I know I said earlier I agreed with y'all, still do, was just doing a quick revisit![]()
I did comply. I calculated my total branch circuit load according to 220.
But 210.19 or 210.21 say nada about adding up receptacles.
Again:
IF Mike Holt, one of the contributors to writing the NEC, says 13 is the maximum allowed on a 20 amp General-Purpose non dwelling occupancy branch circuit that is good enough for me.:happyyes:
If you were asking for a ruling, he would be one of the people you could ask.
Best regards,
Jim
No, it doesn't. 220.14 doesn't say anything about receptacle installations, just load calculations. 220.14 and 220.14(I) both specify minimums, not maximums. To wit:Plain and simple, 220.14 (I) tells you how to calc the maximum number of receptacles that can be installed on a 20 amp or less General-Purpose branch circuit in a non dwelling occupancy.
220.14 Other Loads — All Occupancies. In all occupancies, the minimum load for each outlet for general-use receptacles and outlets not used for general illumination shall not be less than that calculated in 220.14(A) through (L), the loads shown being based on nominal branch-circuit voltages.
(A) Specific Appliances or Loads. An outlet for a specific appliance or other load not covered in 220.14(B) through (L) shall be calculated based on the ampere rating of the appliance or load served.
(I) Receptacle Outlets. Except as covered in 220.14(J) and (K), receptacle outlets shall be calculated at not less than 180 volt-amperes for each single or for each multiple receptacle on one yoke.
No, it doesn't. 220.14 doesn't say anything about receptacle installations, just load calculations. 220.14 and 220.14(I) both specify minimums, not maximums. To wit:
Calculation minimums, nothing about installation maximums.
Yes, as far as sizing the service for the premises, that is the minimum .Larry,
We both agree that 220.14(I) is for calculating the minimum load for receptacles connected to a general purpose branch circuit in a commercial occupancy. Agree?
Where we disagree ,you say 220.14(I) has nothing to do with the number of receptacles that are connected to the branch circuit. Therein, the maximum number of receptacles. You say there is no limit to how many receptacles can be connected to the branch circuit.
Yes, as far as the allowance for the service sizing is concerned. So far, no power is being consumed.Lets say you have 30 duplex receptacles. For calculating the total load for the 30 duplex receptacles you multiply 30 X 180VA = 5400VA.
That is the total calculated load for the 30 duplex receptacles. Would you agree?
Yes, because this has nothing to do with the service calculation. Receptacles are not loads.If the total calculated load is 5400VA, per code, can you connect the 30 duplex receptacles to a 2400VA (120V X 20 amp)20 amp branch circuit?
(That's "cite") As has been pointed out many times, the NEC generally prohibits, rather than allows.If yes, please explain. Please Site the NEC Article where it says you can.
Technically speaking, even the 3 circuits isn't mandated as far as actual installation is concerned.The 5400VA would be divided by circuit VA for minimum of circuits, which is 3, but nothing says how many receptacles per circuit.