I did comply. I calculated my total branch circuit load according to 220.
But 210.19 or 210.21 say nada about adding up receptacles.
Again:
2014 NEC
210.2 Other Articles for specific-purpose branch circuits.
Branch circuits shall comply with this article and also applicable provisions of other articles of this code.
That's as far as I needed to go in Art. 210
Again:
By Mike Holt, for EC&M Magazine
Q1 What is the maximum number of 15 or 20A, 125V receptacle outlets permitted on a 20A, 120V general-purpose branch circuit in a commercial occupancy?
A1 For commercial occupancies, the NEC requires each receptacle outlet to be calculated at 180 VA [220.14(I)]. Therefore, the maximum number on a 20A circuit would be 13. Circuit VA = Volts x Amperes
Circuit VA = 120V x 20A
Circuit VA = 2,400 VA
Number of Receptacles = 2,400 VA/180 VA
Number of Receptacles = 13
Note: According to the NEC Handbook, published by the NFPA, general-purpose receptacles aren't considered a continuous load.
And the number is? 13
Plain and simple, 220.14 (I) tells you how to calc the
maximum number of receptacles that can be installed on a 20 amp or less
General-Purpose branch circuit in a non dwelling occupancy.
If you read 220.14 (J) (1) & (2) there is no limit on the number of receptacles that can be installed on a
General Purpose 15 or 20 amp branch circuit. You can install a 100 15A duplex receptacles on a 15 amp
General-Purpose branch circuit if you want.
Period.
IF Mike Holt, one of the contributors to writing the NEC, says 13 is the maximum allowed on a 20 amp
General-Purpose non dwelling occupancy branch circuit that is good enough for me.:happyyes:
If you were asking for a ruling, he would be one of the people you could ask.
Best regards,
Jim