Really?Originally posted by jwelectric:
It is totally out of the scope of the NEC to say that one article or section will replace another.
90.3 Code Arrangement.
This Code is divided into the introduction and nine chapters, as shown in Figure 90.3. Chapters 1, 2, 3, and 4 apply generally; Chapters 5, 6, and 7 apply to special occupancies, special equipment, or other special conditions. These latter chapters supplement or modify the general rules. Chapters 1 through 4 apply except as amended by Chapters 5, 6, and 7 for the particular conditions.
Chapter 8 covers communications systems and is not subject to the requirements of Chapters 1 through 7 except where the requirements are specifically referenced in Chapter 8.
Chapter 9 consists of tables.
One does not replace the other--where have I said that? But when applying these codes, I address one at a time, in sequence. It goes like this:Originally posted by jwelectric:
The sad part is that you are not reading the articles that you are posting. You seen to be hung on the fact that one replaces the other. This is not true at all.
So at the end of this line of reasoning, where did I have a violation, JW? Where did I demonstrate I "couldn't read code"? I may have simplified it, and added inflection, but didn't I interpret it correctly? Where did I go off track?One of the biggest problems that I run into when teaching a license prep or inspectors is they don?t know how to read the code book. I see that you have the same problem.
That's a big if. If is not "when."Originally posted by jwelectric:
If we use this permissive exception to switch a receptacle as outlined in the exception in 210.52 by the exception itself it is required to be on a general purpose circuit.
...if we don't use the SA as required by (B)(1).which clearly states that this is to be on a general purpose circuit
You're paving the road and not smelling the asphalt! Because 210.70 doesn't care! 210.52 doesn't care either way--if you install a general purpose BC to handle that job, there's an exception to let you. Otherwise, that recep is required to be on the SA circuit!Why do you think that the words ?general purpose circuit? was added to 210.52 and not to 210.70?
My mistake, I should start in 100 when I want to do my lighting layout for a house. :roll:Originally posted by jwelectric:
No George 210.52 comes before 210.70
So then, using that logic, the SA circuits specified in 210.11(C)(1) could not be used to serve the function specified in 210.52(B) if there wasn't a direct reference between them? One box can't serve two purposes? Where is that written?Originally posted by jwelectric:
Bob
The point I was after is that George is trying to use 210.52 to fulfill 210.70.
He can?t see that 210.52 is for the 20 amp small appliance and 210.70 is the general purpose circuit and that they are two separate circuits.
Thanks for the vote of support. How did you convince your class? Perhaps that argument will work against me.Then again it may be impossible to show him anything, I just hate to see others led astray. I have finally got my class to settle down and understand what the code states about 210.52 (B) small appliances
Apparently, by the NEC Style Manual, the CMP agrees with me that requiring an SA is a "basic code rule" and that permitting a GPBC receptacle is an alternative method.3.1.4 Exceptions. If used, exceptions shall convey alternatives or differences to a basic code rule. It shall be the responsibility of the Code-Making Panel to determine whether the principle can be expressed most effectively as a separate positive code rule or as an exception to a rule.
George here is where I just can't understand your view.Originally posted by georgestolz:
One box can't serve two purposes?
Where is it written something can not be down at the same time it is up?Where is that written?
IMO the only purpose of this exception is to allow (not require) a switched receptacle from a GP circuit to be installed in the kitchen, pantry, breakfast room, dining room, or similar area in addition to the SA circuits.210.52(B)(1)Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1, shall be permitted.
Really IMO has little to do with receptacles it has only to do with outlets for lighting.210.70(A)(1)Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
Yes I agree with that as because the ceiling outlet satisfies the requirement for a lighting outlet.Originally posted by jimwalker:
Do we all agree if that dining room had a wall switched outlet in ceiling on general purpose circuit and we pluged in a buffet with light into a SA receptacle that no code was violated ?
Again I agree to some extent.Originally posted by jimwalker:
Only thing is that the customer might prefer the buffet light and not use the ceiling light.That would be there choice.What i have trouble with is seeing how this setup is any safer or dangerious than lieving out the ceiling light outlet.Only differance i see is that we are code compliant.I thought we did not make codes that solved nothing.
See, that's just it. If the code doesn't care what the customer uses it for, then how do you come to the conclusion you do?Originally posted by iwire:
A switched outlet of some type is required by the NEC for lighting, it does not matter what the homeowner uses it for.
Why do you keep saying that 210.52(B)(1)'s exception requires it to be on a GPBC? The difference between "permitted" and "required" is monumentally important to what we're discussing here.Originally posted by jwelectric:
What I have tried so hard to point out to George is that if I am installing a circuit as outlined in 210.52 (B) (1) for the small appliances and decide at this time to switch a receptacle in lieu of the light then I use the exception that is located there which requires that it be on a general purpose circuit.