Re: Switched Din. Rm. Outlet?
Originally posted by iwire:
I have yet to see a view strong enough from the 'other side' that will beat my flimsy opinion.
There's a book on the subject, affectionately titled "Page 24."
JW, I find it amazing that you have progressed to using terms such as "can be" and "permitted" yet come to the conclusion that a separate circuit is required.
Guys, there's no mandatory statement. They're all permissive statements. What prey would the other permitted method be?
Originally posted by iwire:
IMO in this case you can not use one outlet to satisfy two requirements.
What makes this case special to you?
Yes 210.70 is satisfied but your argument is unconvincing as to a 210.52(B)(2).
210.11(C)(1) states clearly that the two SA "circuits
shall be provided for
all receptacle outlets specified in 210.52(B). "Shall" is a mandatory statement. Any receptacle in the areas specified in 210.52(B) shall be on the SA circuits, no questions asked.
210.52(B) slackens the reins a little, but he rule still applies.
A deviation from a rule does not override the rule. An exception does not destroy a code, it pokes tiny holes in it.
That's my answer to 210.52(B)(1) and (2)'s exceptions.
See any code: take 250.68(A), exception 1. Does this entail that every grounding electrode that is driven will be totally buried and shall not be accessible? If a grounding electode connection to a driven electrode is accessible it is in violation?