Re: Switched Din. Rm. Outlet?
George, bless your heart you still have excluded this;
210.52 (B) (1) Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1, shall be permitted.
Edited to add?210.52 (B) (1) is where I am required to install the small appliance circuits and where I find the exception allowing the switched general propose receptacle
This exception allows me to comply with 210.70 (A) (1) Habitable Rooms. At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
With out violating this article 210.52 (B) (2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
Which has only two exceptions
Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electric clock in any of the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired ranges, ovens, or counter-mounted cooking units.
If it was permissible to use the small appliance circuit in lieu of the required lighting outlet they would have added it in one of these exceptions just as it was outlined in the exception in 210.70 (A) (1) Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
Now again I respectfully ask that you explain away these articles and exceptions before I jump the fence. I have been lying in bed counting the sheep that jumped the fence and lost count. This is what happens when I come home and take a two and a half hour nap before supper.
[ April 08, 2005, 01:00 AM: Message edited by: jwelectric ]
George, bless your heart you still have excluded this;
210.52 (B) (1) Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1, shall be permitted.
Edited to add?210.52 (B) (1) is where I am required to install the small appliance circuits and where I find the exception allowing the switched general propose receptacle
This exception allows me to comply with 210.70 (A) (1) Habitable Rooms. At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
With out violating this article 210.52 (B) (2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
Which has only two exceptions
Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electric clock in any of the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired ranges, ovens, or counter-mounted cooking units.
If it was permissible to use the small appliance circuit in lieu of the required lighting outlet they would have added it in one of these exceptions just as it was outlined in the exception in 210.70 (A) (1) Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
Now again I respectfully ask that you explain away these articles and exceptions before I jump the fence. I have been lying in bed counting the sheep that jumped the fence and lost count. This is what happens when I come home and take a two and a half hour nap before supper.